Ok, got a landlord who has a boiler in a outbuilding and wants to prevent the boiler from firing all night due to the internal frost protection activating at 5deg., heating all the pipes to 30deg. He wants to save on fuel consumption.

I've had to install an electrical relay system but need to know whether or not I can de-energise the boilers electrical supply whist its firing. Would this cause possible heat damage to the boiler due to lack of heat dispersal? does the internal pump need to keep running until heat is taken out of the boiler?
 
What you need is a low limit pipe stat on return wired in line with permanent live to frost stat. Temp drops below 5, boiler fires, return hits 30, boiler switches off, simples! :)
 
Not quite what I meant

wants to prevent the boiler from firing all night due to the internal frost protection activating at 5deg, heating all the pipes to 30deg. He wants to save on fuel consumption.

the idea is, he wants to have the pump only run upon activation of a seperate frost stat, therefore reclaining heat from the building in order to keep the pipes warm. He doesn't want the boiler to actually fire. Thus saving the cost of the gas.

all i really need to know is..
whether or not I can de-energise the boilers electrical supply whist its firing. Would this cause possible heat damage to the boiler due to lack of heat dispersal? does the internal pump need to keep running until heat is taken out of the boiler?
 
So you want to modify the internal electrics? I think I would have told him not to be so tight and he may find the gas cheaper than a burst boiler.

Still, good luck with that one.
 
I would agree with SimonG. If he thinks burning gas to prevent the boiler from freezing is expensive what's his next project, disabling the light switches during daytime??
Sounds like a right winner you got there rekab, Watch for the blame game to start if he presses ahead with this foolish idea.
 
Yes you can damage the heat exchanger if you cut the power whilst it is running. As you say the pump keeps running after the boiler has stopped firing to disperse heat from the exchanger and avoid kettling.
 
Not quite what I meant



the idea is, he wants to have the pump only run upon activation of a seperate frost stat, therefore reclaining heat from the building in order to keep the pipes warm. He doesn't want the boiler to actually fire. Thus saving the cost of the gas.

all i really need to know is..

Show the landlord a quote for a replacement boiler due to frost damage,or resite the boiler.
 
disabling the light switches during daytime??

funny you should say that! I already have installed a relay system, for internal PIR sensors with timers internally and with a photocell master outside. works really well actually.(there again he does own alot of properties with communial areas.) Tenants tent to jam time lag switches on.
 
Yes you can damage the heat exchanger if you cut the power whilst it is running. As you say the pump keeps running after the boiler has stopped firing to disperse heat from the exchanger and avoid kettling.

thankyou for answering the question I asked.
 
funny you should say that! I already have installed a relay system, for internal PIR sensors with timers internally and with a photocell master outside. works really well actually.(there again he does own alot of properties with communial areas.) Tenants tent to jam time lag switches on.

I take it the tenants do not pay their own Utility bills then?..
 
Status
Not open for further replies.

Reply to ecoTEC frost protection vs. fuel comsumption. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I would like some guidance regarding the Worcester CDi 29 Classic boiler. According to the manual it has a holiday mode and frost protection mode...
Replies
3
Views
500
Hi I am somewhat confused. My daughter has a combi boiler bought 2-3 years ago and has it timed to come on in morning for an hour and at night...
Replies
2
Views
397
  • Locked
Hi all, Our heating set time is 7:30am off. This morning at around 8:35am the pump started to run, water motorised valve opened, and boiler...
Replies
6
Views
2K
The installation manual says: Frost protection The appliance has a built in frost protection device that protects the boiler from freezing. With...
Replies
0
Views
5K
Hi All, I’ve posted this in general plumbing and realised perhaps that isn’t the correct place. I’m new to the forum and can’t figure out how to...
Replies
6
Views
3K
Back
Top