Can anybody clarify the regs relating to crossbonding. Just had new Vailant Ecotec Pro24 boiler fitted and getting conflicting info re crossbonding. Seems to depend on type of consumer unit?
 
RCD protection for all circuits, both main equipotential bonding conductors have to be present at the gas and water services within 600mm of the gas meter or stopcock before any branch pipework or where practicably possible(10mm green and yellow cable) and a resistance reading of no more than 1667 ohms between pipework, and circuit protective conductors. If all three of these conditions are met supplementary cross bonding can be omitted. Sure others will add some more info
 
Last edited by a moderator:
Thanks for that but still abit confused.
If the consumer board is the old type i.e. fuses rather than RCDs, and as long as the original main bonding is in place, does the new boiler still require crossbonding? I have been told that because of the way new modern boiler are made that CB is not necessary, especially if any plastic fittings/pipes have been used in the installation.
 
if its a new boiler then it has to have it,if its and older instalation then its ncs and you advised the customer that it needs doing and they should get and electirian in to do it if your not part p that my understanding of it
 
agree with above, if the address is wired to 17th edition and all equipotential bonding correct then no suplementary bonding is required at the boiler. if in dobt do it anyway.
 
true but in the 17th regs it also states that if manufacturer says to cross bond then cross bond it is cheers
 
Status
Not open for further replies.

Reply to crossbonding in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have a 40 year old floor standing Glow Worm 45-60 boiler (open vent )which is in a cupboard in the centre of the house. Its an old workhouse...
Replies
2
Views
377
We are considering buying a house which currently has a 20 year old Ideal Icos boiler, so we're factoring in replacing the boiler soon. Current...
Replies
2
Views
504
I recently had a new 2023 Vaillant ecoTec plus 630 (30kW) system boiler installed along with a Low Loss Header (LLH) in my house. I have 21 rads...
Replies
10
Views
827
[ASIDE: I did wonder if this was the best forum for this but figured as it was a boiler related issue that the gas engineers would be dealing...
Replies
5
Views
284
Hi all. So I have just moved into a new house with a Potterton boiler in it. Great big thing!! lol. I want to fit a Hive to it but it obviously...
Replies
16
Views
2K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock