Hi,

I have a blocked 10mm pipe to a Towel Rad. I have both ends disconnected (distribution manifold and Rad) but cant get any flow through it. I have tried mains hose on to one end, but it seems to hold firm.

Its never works since I've been in the house (18 months) and the property is aprox 15 years old. There has been historic magnetite in the systems, but I have drained/filled it a couple of times when I moved in, I have been operating magnetic filters and used a course of X800 and have Inhibitors in normally.

Its not the only rad with a flow problem, but I'm addressing them one by one by flushing just the One Rad circuit at a time from the distribution manifolds. See picture.
Cylinder Room .jpg

Ant thoughts other than replace the pipe or replumb the house ;-) ?

Many thanks
 
Adapt a foot pump or compressed to fit it. 8mm is a snug fit, so you'd have to put 10mm to 15mm adapter on and then a 15mm to 8mm. And then pump away.
 
as above and watch your pressure tho

the only other way you could try is putting some cleaner do there and see if that weakens it
 
I've always found these with near boiling water is good for dislodging most sludge. Just be careful of fittings blowing off. (its not fun when they do that)
 

Attachments

  • 51OvEW0tD7L._SX355_.jpg
    51OvEW0tD7L._SX355_.jpg
    22 KB · Views: 121
Last edited by a moderator:
I've always found these with near boiling water is good for dislodging most sludge. Just be careful of fittings blowing off. (its not fun when they do that)

What is the name of that device. I'd like to try that

Thx
 
Also adding fairy liquid and leaving it sit pressurised for a while seems to help.
 
Ok finally received my Pressure Tester courtesy of Amazon. :vanish:
image.jpg
i have it connected to the now disconnected 10mm feed from the 22mm 4 Port distribution manifold. The pipe runs use the floor and downstairs through the bathroom wall to the offending Towel Rad. I have also disconnected the check valve from the Rad so I have an open 10mm copper pipe with 15mm reducer.
image.jpeg

When I pump the pressure tester I have had a small amount of water seep from the open 10mm pipe at the Rad, but it's losing pressure. I've taken it up to 15 bar, but no more for fear of blowing the plastic to copper joint behind the tilled wall. It very very slowly loses pressure but has not pushed the blockage out.

Any suggestions on the best way to deal with this ?

Many thanks....
 
Last edited:
Try pressurising from the other direction- towel rail end
 
Finally unlocked it !!

I repeatedly pressurised it up to 10 bar with the pressure tester. In each cycle it took a bit extra water that would drip drip out the end. I then switched the pressure tester water over to a bit of neat X800 to push that through to the blockage area.

Finally after a few hours of pushing it through, the pressure blew out a plug of black crystals and sludge. Fortunately it did not hit the bathroom ceiling ;)

Now I've washed the heating loop through with mains water and it should be ready to reconnect tomorrow.

I think the pressure tester advise has saved a rip out of the pipework from the walls. Thx for all the advise.
 
And thank you for keeping us updated and letting us no your problem has been sorted
 
Had a bit of a leak on one of the 4 port Speedfit manifolds, but fixed that with a good cleaning and polishing the 22mm pipe.

image.jpg


I now have good heat flows in all but one of my rad circuits, except one rad. Fortunately the original Blocked Towel radiator is now working perfectly.

image.jpg
image.jpg

Whilst I have flushed it with mains water as well as X800 and thought it was heating well, it appears that there is some blockage. Does anybody know how this type of rad flows ?

Looks like I may have to remove it for a bit more of an aggressive cleaning process. Perhaps with a pressure washer in the garden.

P.S. the FLIR One thermal camera for the iPhone is amazing. Diagnoses any problems with flow and has enabled me to map my UFH circuits.

Cheers Bob
 

Attachments

  • image.jpg
    image.jpg
    23.4 KB · Views: 26
Last edited:
image.jpg

should be ok now
 
Status
Not open for further replies.

Reply to Blocked 10mm Speedfit Pipe to Towel Rad in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
339
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
234
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
252
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock