Discuss Anti vac trap in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.

townfanjon

Esteemed
Plumber
Gas Engineer
Subscribed
Messages
8,642
Evening chaps , never done this and it's all going behind a long wet wall.
A nats over 3 meters long horizontal soil pipe what has a ok 'fall' joints an internal soil pipe.
On the run are 2 toilets and 2 basins, rather than run 2 separate basin wastes all the way back to the soil pipe.
Can I use 2 anti vac traps on the basins and just use 2 strap on boss's with 2 short lengths of waste straight in to the pipe.
Thank you
 
When we do this we use antivac traps, stops the other gurgling when one basin is let go, cheaper than using hepvo's to. As said upsize it to 1 1/2'' waste pipe to.
 
50mm wastes come on boys.... I would also run a 32mm vent back to the stack from an years facing tee between the sinks .

Worked for 100 years before fanny traps and anti symphonic
 
Last edited by a moderator:
50mm wastes come on boys.... I would also run a 32mm vent back to the stack from an years facing tee between the sinks .

Worked for 100 years before fanny traps and anti symphonic

50mm is oversized for two basins in a domestic property? Have fun chopping that in the wall!
 
Status
Not open for further replies.

Reply to Anti vac trap in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock