When I turn on our CH there's a lot of noise from one specific part of the system - the pipes on the landing, and one radiator. It sounds like air, and the landing radiator needs bleeding regularly (about once a month), even though it isn't the highest point in the system. The two upright rads in the bathrooms are a good 50cm higher but rarely have more than a quick "pfffft" of air if I open the bleed valves. All the radiators get hot from top to bottom (except when the landing one needs bleeding) and the noise stops after a couple of minutes running.

Wondering what could be causing one radiator to fill with air so quickly, and why there could be so much air trapped in one part of the system. I can't see any sign of a leak. Any ideas?
 
Have you a sealed or open vented system?
You'll have to forgive me - I'm not great with the terminology - but I think it's vented. There's a dome-shaped air separator at the highest point in the airing cupboard, out of the top of which comes a pipe that goes all the way to the header tank where it curves over the tank. The system was installed around 1990, although the boiler has been replaced within the last ten years. When the boiler was changed a Valiant magnetic filter was added, and this has been drained a few times.
 
You might post a photo of that, it sometimes gets full of sludge causing those problems you are getting, if your boiler is a heat only boiler it will have a circulating pump installed close to this and after it, the boiler would be the "4" series like a 418 or 424 etc, if so post a photo of this pump as well.
 
Boiler.jpeg

This is the boiler. It was installed about eight years ago. It's been maintained pretty well and has a magnetic filter installed above it.

Separator.jpeg

This is the separator in the airing cupboard. I used a very powerful magnet to try and dislodge anything clogging it up. The magnet did something because you could hear stuff moving and going down the pipe when it was released. I did this a few times until there was no more sound when it was taken off.

pump.jpeg

This is the pump. It’s below the separator (about 20cm). Between the separator and pump is the feed which comes down from the header tank. The pump was changed when the boiler was installed, so is also about eight years old.
 
Try and look into the small feed and expansion tank in the Attic and see if water is flowing out of the vent pipe or drawing air into it, you will have to hold a "glass" full of water with the vent pipe immersed in it to see this. If neither, get someone to start the boiler and see if any spurt of water from the vent, then get them to stop the pump and watch again for any spurt of water, you may have to wait for ~ 3 minutes for the pump to stop after boiler switch off.

How may rads have you got?
 
Try and look into the small feed and expansion tank in the Attic and see if water is flowing out of the vent pipe or drawing air into it, you will have to hold a "glass" full of water with the vent pipe immersed in it to see this. If neither, get someone to start the boiler and see if any spurt of water from the vent, then get them to stop the pump and watch again for any spurt of water, you may have to wait for ~ 3 minutes for the pump to stop after boiler switch off.

How may rads have you got?
I'll give that a try.

Sixteen rads. Two have never worked. We had the system power flushed when the boiler was fitted, and we were told this would sort it, but it didn't. One is in the hall and the other is a small secondary rad in the living room, so it's never been a big deal, but there are problems somewhere.

I go around with the key a few times a year, but most rads have no air or just a tiny bit. It's only the one noisy rad that seems to fill with air, but thinking about it, that might be the first one the pipes go to. It's the closest to the air separator/pump.

The pipework to the rads is microbore. Does that make them more likely to block with crud? I assume it does.
 
If you're prepared to flush the system you could leave some system cleaner in there for a few weeks while the CH is on and see it that unblocks anything. I'll leave John to advise about the F/E tank and pump but I'd seriously consider getting the system sealed, it does save alot of ball ache with air ingress.
 
I had a similar problem, air building up in the boiler, power flush temporarily solved it but after a couple of months the problem returned. Called a local company who sent an engineer and they claimed the heat exchanger was blocked due to the system being fed through a water softener. Viessman technical told me that was rubbish and that they recommend feeding the system with softened water as the heat exchanger is stainless steel. The company then told me that a replacement heat exchanger was not available. Turned out that the engineer had got the model number garbled and Viessman confirmed that the part was available. The company quoted £2500 to replace the boiler.
Needless to say at that point I threated to report them to trading standards and refused to pay their callout.
I then decided to try to fix it myself, having studied the installation guide I found that it was incorrectly installed. The pump is on the wrong side of the boiler and it was fed with a switched live from the thermostat to the permanent live on the pcb. I rewired it (I am a qualified electrician) and now it is working fine.
 
Hi to John.g.
You recommend ...Try and look into the small feed and expansion tank in the Attic and see if water is flowing out of the vent pipe or drawing air into it, you will have to hold a "glass" full of water...

I can do this test, as my CH system that has a similar issue, but only at the bathroom radiator.
Please can you enlighten me on what the outcome proves and what the solution would be?

As I have noticed the copper pipe that runs upto the expansion tank gets warm /hot. would this draw air the the system as it cools down?

Best regards
 
Hi to John.g.
You recommend ...Try and look into the small feed and expansion tank in the Attic and see if water is flowing out of the vent pipe or drawing air into it, you will have to hold a "glass" full of water...

I can do this test, as my CH system that has a similar issue, but only at the bathroom radiator.
Please can you enlighten me on what the outcome proves and what the solution would be?

As I have noticed the copper pipe that runs upto the expansion tank gets warm /hot. would this draw air the the system as it cools down?

Best regards
Have you the same vent/cold feed arrangemant as Richtop8 above or something similar without the "dome",
depending on what arrangement you've got you may have to cut out a section and throw away the dome (think its called a Airjec or something like that, as sludge builds up in it)

Before doing anything look at your pump and check its mode & setting, if it has LEDs and you are unsure what they show, just post a close up photo of them wthe pump/boiler running. It may be set too high.

How mant rads??.
 
Hi good afternoon l
My CH system has 10 rads.

I do not have a "dome" arrangement, the expansion goes via 25mm copper pipe to the expansion header tank. It has a bend downwards and an air gate to the surface of the liquid.

The Pump is a Grundfos type: UPS2 15-50/60. It has 3 pump settings low, medium and high.
On the low settings I get less air than on the medium and most air on the high setting.

It is presumed to be air as it is not flammable gas.

About 5 years ago I flushed out the CH system by taking out the Grundfos pump to get access to the connections for the circulating pump instalation. There were no leaks during the circulation cleaning period. So I presumed all fittings were sound and leak free.

Do you have any observations on what causes the air ingress and how to fix it?

Thanks
 
Hi good afternoon l
My CH system has 10 rads.

I do not have a "dome" arrangement, the expansion goes via 25mm copper pipe to the expansion header tank. It has a bend downwards and an air gate to the surface of the liquid.

The Pump is a Grundfos type: UPS2 15-50/60. It has 3 pump settings low, medium and high.
On the low settings I get less air than on the medium and most air on the high setting.

It is presumed to be air as it is not flammable gas.

About 5 years ago I flushed out the CH system by taking out the Grundfos pump to get access to the connections for the circulating pump instalation. There were no leaks during the circulation cleaning period. So I presumed all fittings were sound and leak free.

Do you have any observations on what causes the air ingress and how to fix it?

Thanks
 
Hi apologies
The expansion copper pipe is 15mm not 25mm...finger trouble :)
The vent pipe is/should be 22mm and the cold feed is 15mm, are you sure its not the cold feed you are looking at.
Is the pump located upstairs in the hot press and the boiler downstairs, if so, and if you have zoned CH and HW then you will have at least two motorized valves fairly close to the pump, they may be located above the pump or below it, between the pump and these you might see something like the above arrangement (without the air jec).
Also go to the attic and have a look at your small cistern (Feed & expansion or F&E cistern for short) and see where the vent goes up and over it and also the cold feed which will come from the side or end of this cistern, you can then follow it and see where it is teed into the system.

Might look something like this: (This pump is pumping downwards)

1709661238401.jpeg
 
Last edited:
Apologies for the delay in replying.
F&E tank photo attached plus images of:
Grundfos pump set at lowest speed
2-way Motorised valve and controller also shows 15mm F&E feed.

Do you recomend the "glass" of water test on the 22mm vent pipe.

I presume that if the water is sucked into the vent that is where the air gets in.

Any other thoughts?
Thanks
 

Attachments

  • 20240306_170959.jpg
    20240306_170959.jpg
    295.9 KB · Views: 15
  • 20240305_163526.jpg
    20240305_163526.jpg
    294.6 KB · Views: 19
  • 20240306_071957.jpg
    20240306_071957.jpg
    236.2 KB · Views: 18
For clarification
15mm F&E pipe
22mm vent pipe
Gas boiler is downstairs, pump upstairs in the hot press.
Zoned CH and HW with a 2-way Motorised pump and controller.

Thanks again.
 
That Drayton 3 way mid position valve installation doesn't look right to me, can you check that the direction (up or down) the pump is pumping, there should be a arrow on the pump body, also there may be AB stamped on one the valve body ports and maybe a A & a B on the other two, B should go to the cylinder heating coil inlet (top) and A should go the the rads.

1710350944082.png
 
Hi good evening,

TheGrundfos pump arrow on the front is pointing anticlockwise so is pumping up.

I removed the Drayton 3 way mid position motor controller to check if marked A or B and it was not marked.
 
Hi good evening,

TheGrundfos pump arrow on the front is pointing anticlockwise so is pumping up.

I removed the Drayton 3 way mid position motor controller to check if marked A or B and it was not marked.
See image sent. The arm is shown in the down position = Central Heating. Whin the controller moves the arm a 1/4 turn up it is in the Domestic Hot Water position.
 
Still looks wrongly plumbed to me, it should, IMO be like shown below.

The pump outlet might be connected to the CH

Can you confirm or not that the cold feed is teed in to where I have the labeb, if it is then definitely plumbed incorrectly.

Others might comment??

EDit: I can't post a photo either so

Can you confirm that the pipe teed into what you caal the CH pipe is the cold feed, if it is then plumbing definitely incorrect.

Will try and post photo later.
 
I can confirm that the 15mm pipe on the Left side is the F&E cold. This is T-eed into the CH 22mm pipe from the left side of the 3-way Drayton midposition valve.

The boiler feed comes through the floor to the bottom of the 3-way Drayton midposition valve.

The DHW to the cylinder coil comes from the top of the 3-way Drayton midposition valve .

How would this configuration cause the excessive air in the Central Heating system?

Thanks
 
OK, can you post a close up photo of the Drayton data label, we will then see, once and for all, what way the 3 ports are positioned.

You said the "TheGrundfos pump arrow on the front is pointing anticlockwise so is pumping up." can you post a photo of this, the arrow is normally on the side of the pump body and points either straight up or straight down. Sometimes, rarely, there may not be a arrow but if you look at the black asterisk I have placed in both photos below, you can determine from the ridge/bulb on the pump body which direction its pumping in as the start of the ridge will be closer to the pump inlet.

Can discuss the excessive air later depending on findings, above.
 

Attachments

  • Pump pumping upwards.jpg
    Pump pumping upwards.jpg
    271.7 KB · Views: 8
  • Pump pumping downwards.jpg
    Pump pumping downwards.jpg
    271.6 KB · Views: 11
Last edited:
Apologies for butting in - I am interested! The Drayton/Invensys valve seems not to be a mid-position type.
Does the symbol on the side suggest: in 1, out on 2 or 3? (or that's what the plumber thought!?)
Most suppliers are saying it's "obsolete" (apart from the above) and I can't find a data sheet or spec 🤔
IMG_0500.jpeg
The actuator below is just 2 position:
And yes, too much time on my hands on a weekend morning! 🤪
 
Last edited:
It mustn't be, as the the normal type is like a T with the pump pumping into the T "bottom" and the CH & HW on top of the T, however, its worked for years apparently but the left hand pipe to the CH has the cold feed teed into it, if it is like the traditional 3 port then the pump is pumping into the CH port A, if CH only selected or both CH&HW then it will work but if HW (port B) only selected then port A will be closed and the pump will be running against a closed valve with no flow to the HW coil or something like that which would surely have been noticed.
 
Apologies for butting in - I am interested! The Drayton/Invensys valve seems not to be a mid-position type.
Does the symbol on the side suggest: in 1, out on 2 or 3? (or that's what the plumber thought!?)
Most suppliers are saying it's "obsolete" (apart from the above) and I can't find a data sheet or spec 🤔
View attachment 87531
The actuator below is just 2 position:
And yes, too much time on my hands on a weekend morning! 🤪
Just noticed that 2 position now, you can get a 3 port diverter valve (2 position) or a 3 port (mid position) valve.
 
Just noticed that 2 position now, you can get a 3 port diverter valve (2 position) or a 3 port (mid position) valve.
I'm familiar with 3-port mid position etc etc. Basically I was coming to the conclusion that this early commercial Drayton is a 2 position diverter, supported by the symbol on the side, the fact that the actuator seems to be 2 position, and thus concluding that the basic plumbing (ie the pump position) might be correct for this particular valve?
And I tried to offer some evidence to support the theory, given that the OP hadn't provided pics that could fully identify the valve and actuator.
 
Last edited:

Reply to Always lots of air in our CH system in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
322
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
231
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
243
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
231
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock