Hi all,

Was wondering if anyone had come across this before or might know what the problem is.

Trying to adjust the air gas ratio on a 28i junior. Put it in service mode. Turn the dial to maximum. Boiler goes to full output. Adjust the valve to get the reading I need. All good. Then turn down to minimum and the boiler won't stop modulating up and down so impossible to get a reading to adjust the gas valve.

Anyone got any ideas?

Many thanks,

Nat
 
Hi all,

Was wondering if anyone had come across this before or might know what the problem is.

Trying to adjust the air gas ratio on a 28i junior. Put it in service mode. Turn the dial to maximum. Boiler goes to full output. Adjust the valve to get the reading I need. All good. Then turn down to minimum and the boiler won't stop modulating up and down so impossible to get a reading to adjust the gas valve.

Anyone got any ideas?

Many thanks,

Nat

what readings you getting on low? From to etc? What gas valve prettle or sit?
 
The gas valve may be so out of range its modulating because if that. I had one once that I could not get a reading off.

The best way to get there is to turn the boiler off and wind down the gas valve on high and low and adjust it that way.

When you first fire up the boiler it won't light until you start adjusting it.

Failing this I'd say its probably something pcb related, or electrical related atleast.
 
When you say modulating, is the fan speed going fast then slow or is the boiler cutting off, then firing back up? May well be that the gas valve after setting the high up, is now out of adjustment on low so much that it won't remain alight on minimum. If you call Worcester, they should give you the instructions on how to 'reset' the gas valve back to it's factory settings. You can then start all over again with the adjustment.

If the fan speed is going fast and slow, could be the fan is about to completely go. My guessing would be the gas valve adjustment though.
 
Here are the factory set gas valve settings that worcester will tell you. Print this off and use this, save on expensive phone calls to worcester :)
p
 

Attachments

  • image.jpg
    image.jpg
    93.2 KB · Views: 25
The above post is for a sit gas valve, but I found those more common anyway :)
 
you need to start from low flame

when you say modulating I am sure boiler does not fire and then fun clears burning chamber

put boiler on ch and turn thrmostat on 2 and then keep analyser in and adjust when stable and happy put to service and do the same
and after pls recheck low flame again just to be 100% sure
 
Yes agree with above, sounds like the gas valve had been incorrectly adjusted. My bet is the 4mm has been adjusted on max, then the boiler won't stay lit on minimum so ramps up to fire, then drops down, goes out, repeat etc.

9 times out of 10 you can turn the 4mm clockwise 1 full turn and it will be enough to stay lit and go from there.

allways adjust max first as its does have an effect on min settings, whereas min (4mm) does not have an effect on max once set.
 
Last edited:
Status
Not open for further replies.

Reply to 28i Junior modulating in minimum mode in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have read that an Auto Bypass Valve (ABV) is not compatible with a pump set to Proportional Pressure (PP) mode. I have a recently fitted...
Replies
6
Views
2K
Hello, We got a Vaillant Ecotec Exclusive Green IQ 835 combi boiler in November 2021 as we wanted the most efficient boiler that modulated really...
Replies
4
Views
2K
Good morning all, just a quick one here and i was wondering if someone could give a little advice on their own experience. I don't usually do a...
Replies
2
Views
513
    • Like
Hi everyone, Just wanted to share my experience with "upgrading" an S plan setup to Opentherm and Vaillant Control Center (VR66). There are a few...
Replies
1
Views
1K
Hi all I wonder if anyone could offer some advice. I’m looking for a new combi and thought I may as well upgrade to smart controls if we have to...
Replies
7
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock