Been having some trouble with intermittent hot water in the showers/taps for a while now (was working for a couple of years normally but been getting progressively worse). At one point cold water was coming out from the hot taps.
I have a Worcester Bosch boiler and an unvented Megaflo system...
prash123
Thread
cold
cold water
coming
hot
megaflo
system
tap
taps
water
Firstly this a great forum, this is my first post but I been an observer/reader for a while! OK so back to questions at hand.
The house:
I bought a new house around 1970s build 4 bedrooms full refurb. New radiators and pipework. Plastic pipe under the floor leading to copper coming out of...
Got to call in to one of these bags of poo tomorrow morning!
only dealt with on the phone, she says fault code is no flame detected. The boiler is about 3 years old.
probably never been serviced.
im thinking service, clean ionisation sensor amd electrode, clean and check condensate?
anthing...
Any thoughts on putting a 2 port on a megaflo return, which has a 3 port only set up.
There is no room or pipework space to get it on the flow to cyl after the 3 port. Whoever fitted it must have thought the 2 port was a billy bonus for stock.
My thinking is better on return than not at all.
Hi - the T&P valve on my Megaflo is dripping from the valve marked T&P on the outer right hand side of the system, and has been for about 18hrs. At one point it was quite heavy, but now it is a steady, but slow drip. This system is about 2yrs old and there have never been issues before.
My...
Hi guys,
Installed a new towel rad in a new loft bathroom on a megaflo system now being asked if I can now connect it up so it heats up when the heating is off for summer use....how?
Was thinking the dual fuel CH/Electric element, but builders are saying there's another way...
Any...
RAW85
Thread
could
electric
element
help
megaflo
towel
towel rad
Went to this job today and was there quite a while, it's a baxi boiler, unvented cylinder upstairs.
I get get there, boiler works fine on ch, put how to constant nothing, light comes on at programmer but no 'click' sound. So quick job swap programmer over - no change.
but if I turn he to...
Out of the blue recently we are experiencing an odd vibration from or near our Megaflo Cylinder. The noise occurs when toilets are refilling after flushing (doesn't matter which one) or when the washing machine/dishwasher is taking water. It appears to be coming from either the cylinder itself...
I have a megaflow system and have noticed that if I pour a glass of hot water and leave it to stand that small white particles are floating in the water at the top of the glass. Any ideas what this could be of what may be causing it?
Thanks
Got a big job coming up. Its a big old house in Chelsea and customer is no holds barred on cost!
Its currently got a Keston C90 light commercial boiler, 2 linked copper cylinders (210l each approx) honeywell wireless programable room stat and 2 channel programmer. heating on one zone.
Im...
Hello;
I have a Gledhill Boilermate 2000 and a Micron 60ff boiler. The Boilermate has 2 unrepairable leaks and i need to replace the system.
Is a Megaflo system a suitable alternative? a few plumbers have mentioned that system and just want to check it will do all that the boilermate does...
johnnypiano
Thread
boiler
boilermate
boilermate 2000
getting
megaflo
oil
replace
suitable
system
Hello
I am hoping for some advice please. I have recently noticed that my stop tap under the kitchen sink is really tight, so to check we can isolate the supply in an emergency I turned off the stop tap in the road - all OK. However, when turning it back on I noticed the 0.0001 dial is...
Chris80
Thread
found
leak
megaflo
meter
movement
slow
turning
water
water meter
Heatrae sadia megaflo is showing a visible flow through the tundish.
The water is stone cold through the tundish.
Combination valve has already been replaced.
Recharged cyl countless times.
Cheers
Hi guys.
Had a dripping through the discharge pipe, visible through the tundish for ages.
Tried recharging the air gap to no avail.
Had the 3 bar sustaining valve and 8 bar PRV valves replaced and it still done it.
Forgot about it for a while, but now its actually running through the...
We are considering installing a megaflo system as part of our bathroom upgrade. The water pressure is 2.8 bar. The plumber will have to install the cylinder into a cupboard which has 2 outside walls but is accessed through a door in one of the bedrooms. Is there any noise associated with...
Hi,
I need to replace my combi boiler with a new boiler and unvented cylinder. Which boiler do you prefer Worcester Bosch or Vaillant?
Which unvented cylinder do you rate, Megaflo or other?
Thanks.
LCV
Thread
boiler
cylinder
megaflo
new boiler
oil
other
vaillant
We're having boiler problems with our Gloworm 30SXI which is 10years old (its been a nightmare since we purchased the house new with many parts replaced), and I now have to decide whether to repair the boiler again (looking at £200+) or replace the boiler. Someone who owes me some money has...
I have a megaflo hot water tank fitted with red expansion tank with gauge and relief valve fitted on top ... My problem is
water is continually discharging from overflow. The Gauge used to read 2 BAR now reading 3.6 - if I reduce the pressure using the relief valve on top of the gauge the...
Silly grandad
Thread
cylinder
gauge
heating
hot
megaflo
pressure
problem
tank
water
weather
Customers 5 year old megaflo has a faulty baffle, it's dropped below the tpr hole & is stuck in that position.
Heatrae Sadia say that it's only the stainless cylinder thats guaranteed for 25 years and not any of the parts inside the cylinder.
Just wondered if any one has had a similar problem...