Messages
56
Hello all,

Just moved into a house with a Vaillant EcoFit Pure 835 boiler that is 3-4 years old but the previous owner did not bother to register with Vaillant, so Vaillant says its not under warranty.

I've noticed that despite setting the CH to 60 degrees on the boiler's control panel, the boiler heats to 75 degrees with the radiator LED blinking. The DHW is set to 50 degrees but I am pretty sure the output from boiler is much hotter than that.

Can someone please clarify what is happening here and how can this be fixed?

Thanks.
 

Attachments

  • 1674828620101.png
    1674828620101.png
    361 KB · Views: 9
  • 1674828701642.png
    1674828701642.png
    181.6 KB · Views: 8
Thanks for your replies.

I have a wireless room thermostat which is called Vaillant VRT 350F. On this device, I have desired room temperatures set to 18 degrees only when the heating is ON.
I am not aware of any other setting. Kindly advise.

If the room thermostat is responsible, is there a way to take its batteries out and start the CH on the boiler itself after bypassing VRT350F? This can establish if the boiler panel controls are working on their own.

Also, this does not explain why the DHW is so hot!
 
Thanks for your replies.

I have a wireless room thermostat which is called Vaillant VRT 350F. On this device, I have desired room temperatures set to 18 degrees only when the heating is ON.
I am not aware of any other setting. Kindly advise.

If the room thermostat is responsible, is there a way to take its batteries out and start the CH on the boiler itself after bypassing VRT350F? This can establish if the boiler panel controls are working on their own.

Also, this does not explain why the DHW is so hot!
The VRT 350 is capable of load compensation as far as I remember.
That means that it can regulate the boiler temperature by overriding the boiler settings.

Thinking of the room where the VRT is situated:

Is the room reaching temperature quick enough?
Once it is up to desired temp, does it remain comfortable and if so are the radiators still very hot?

It may be that the radiator where the sensor is, is undersized? or could it be in an area/room that never reaches the desired temp for some other reason?

It is difficult without seeing the set up you have but worth a try.

Have you tried siting the sensor in another room/area to see how it performs.
 
The VRT 350 is capable of load compensation as far as I remember.
That means that it can regulate the boiler temperature by overriding the boiler settings.

Thinking of the room where the VRT is situated:

Is the room reaching temperature quick enough?
Once it is up to desired temp, does it remain comfortable and if so are the radiators still very hot?

It may be that the radiator where the sensor is, is undersized? or could it be in an area/room that never reaches the desired temp for some other reason?

It is difficult without seeing the set up you have but worth a try.

Have you tried siting the sensor in another room/area to see how it performs.
I have the VRT350 manual somewhere so I will check on this load compensation.

As the thermostat is wireless, it tends to stay in multiple rooms.
The radiator valves in 2 rooms are already closed to conserve energy, but the other radiators are getting hot enough, apart from one that is farthest from the boiler. The twin radiator nearest to the boiler gets very hot very soon.
The balancing on the system is quite bad and I am partially responsible for that, but I never realised that this could lead to boiler overshooting the temperature set at its own panel!

If there is a dummy guide on radiator balancing, please do share. Thanks.
 
Try to keep the control in one place. Maybe the living room.
Some controls (not sure about yours as we use the sensocomfort now) can be optimising as well as load compensating.
If it is attempting to 'learn' how quickly your property takes to reach a desired temperature, keep moving it won't allow it to work correctly. As I said, i can't remember whether or not the VRT 350 does that or of it just uses load comp.

A week in one place may show a difference. 1.5 meters up and away from heat sources is good.
Failing that, you'll need to get someone out to look at it and balance system.

Vaillant literature is all on their website if you need it.
 
A week in one place may show a difference. 1.5 meters up and away from heat sources is good.
Sorry for late reply. This advice did not help unfortunately. The VRT350F has been on a 1.5 meter high shelf for ~3 months and it did not make an iota of difference to temperature or behaviour.

Just had the boiler serviced and the engineer told me that despite the display on the boiler, the water being circulated might be 65 (which is my control panel setting on the boiler). He was clueless when I told him that regardless of temperature settings on the control panel, the radiator always got heated to the same temperature.

There is an option of resetting VRT350F which should lead to installer menu, but the service engineer was not keen on that. I understand that as the VRT550F user manual says that boiler will not fire unless it is setup properly.

Should I focus on getting some help from Vaillant here? Would they even help me as I am not an installer?
 

Reply to Vaillant EcoFit Pure 835 Temperature Panel Control in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
248
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
317
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
229
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock