helllooo every1,

im asking a bit daft question but i hope you can help me out here.

i was tring to gas rate a main 25 he boiler but it kept on modulating, how do we set these to service mode so we can gas rate them on full power? dont have MI
cheers guys.:rockon2:
 
Run ho****er at max rate?


Sent from my iPhone using Tapatalk
 
Need bit more info on exact boiler model. Is it newer one with zero governor-Combi eco 25?
 
simons, ive run it on full water mode but i know it modulates when the fan speed reduces

graham yes its the new combi eco 25he

thx
 
Well it is the same as a Promax HE then. All heating controls calling. Heating & water temp knobs fully off. Turn HW knob quarter turn twice quickly. CH knob now round fully clockwise. Take your G/R & FGA. Job done.
 
Well it is the same as a Promax HE then. All heating controls calling. Heating & water temp knobs fully off. Turn HW knob quarter turn twice quickly. CH knob now round fully clockwise. Take your G/R & FGA. Job done.
is that the same with the baxi solo then?.
 
Status
Not open for further replies.

Reply to modulating valve setting in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the...
Replies
5
Views
333
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
562
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason...
Replies
3
Views
343
Back
Top