I had a solar thermal cylinder installed last week.

The installers had an issue with one of the valves and installed a 15mm pipe (see red arrow in picture) instead of the 22mm at the valve. Is this going to be an issue?

The 15mm then feeds into the larger 22mm. However, my concern is that I am away frequently so if pressure builds up and the water needs to escape there could be a lot of force on the 15mm piece and section.

Thanks for any input.
 

Attachments

  • Cylinder 15mm R.jpg
    Cylinder 15mm R.jpg
    372.8 KB · Views: 34
The installers initially cross threaded the 22m and then switched to the 15mm. Do you think this will be an issue in the future? How likely is it that you need to change from one output point to another?

Also, the pipe work now blocks access to the pump and Honeywell valve - will that cause an issue in the future? I have attached another picture.

Separately, I noticed that the dump pipe goes up initially (you can see it isnt horizontal or downwards in the photo), this will mean water will run backwards or stay in the pipe - is that an issue?

Thanks.
 

Attachments

  • Full System C.jpg
    Full System C.jpg
    390.3 KB · Views: 28
I'm not too familiar on solar thermal installations, so there's only so much my words can be warranted. If the combined temperature and pressure release valve is designed for 22m outlet pipe to D1 of the tundish (which I cant see either) then it should be 22mm and at least one pipe size bigger after the tundish, depending on length of run to termination.
As for running slightly uphill, you are correct, this will create a restriction in the flow of water trying to be dumped for obvious safety reasons.
The pipework blocking the pump will, as you say cause problems if/when the pump fails.
Overall I'm not too impressed looking at this and advise seeking remedial work by someone more competent.
 
I have attached a video from the outlet to the tundish. The pipe after the tundish does look bigger. How can find out if "the combined temperature and pressure release valve is designed for 22m outlet pipe" - should I look on the valve somewhere? I have also attached a photo of the tundish area,

Thanks for your help.
 

Attachments

  • 20210519_150514.mp4
    9.7 MB
  • Tundish Area.jpg
    Tundish Area.jpg
    424.3 KB · Views: 22
That arrangement looks all wrong. D1 into tundish should not exceed 600mm, which that does. D2 after the tundish should be 300mm minimum before the first bend and at least one size bigger, which it is to be fair.
The valve does look like it's designed for 22mm and has been packed out with 15mm to make a seal.

I can even see a slight weep where its not perfectly sealed.
 
Are you saying that an installer damaged a factory-installed 22mm temperature/pressure relief valve and replaced it with a 15mm one? If so, I'd want to check with the cylinder manufacturer whether this is okay, and I'd expect the answer to be 'No.'

I think you need the system to be looked at by someone who knows what they are doing.
 
Are you saying that an installer damaged a factory-installed 22mm temperature/pressure relief valve and replaced it with a 15mm one? If so, I'd want to check with the cylinder manufacturer whether this is okay, and I'd expect the answer to be 'No.'

I think you need the system to be looked at by someone who knows what they are doing.
I heard them say that they had cross-threaded the 22mm and couldn't get it on. Then the other one suggested using a 15mm. I have emailed the manufacturer to ask about the outlet pipe.

I do know that it is not meant to go upwards (as it does on the right-hand side) so that is definitely an issue. The pump and Honeywell valve being inaccessible is also an issue.

Once I have enough potential issues I will speak to Gas Safe so that they confirm if the installer was G3 qualified or not. He clearly has not thought the installation out.

A friend stated that the outlet had to drop 300mm before turning off but looking at the regulations online it seems that applies after the tundish and not before.
 
I heard them say that they had cross-threaded the 22mm and couldn't get it on. Then the other one suggested using a 15mm. I have emailed the manufacturer to ask about the outlet pipe.

I do know that it is not meant to go upwards (as it does on the right-hand side) so that is definitely an issue. The pump and Honeywell valve being inaccessible is also an issue.

Once I have enough potential issues I will speak to Gas Safe so that they confirm if the installer was G3 qualified or not. He clearly has not thought the installation out.

A friend stated that the outlet had to drop 300mm before turning off but looking at the regulations online it seems that applies after the tundish and not before.

That 300mm applies after the tundish. D1 to tundish is a max of 600mm and obviously can rarely be achieved without a bend or two.
 
Yep that’s a no from me also who installs a 2 port so you can’t service it wants ripping out and starting again
 
Yep that’s a no from me also who installs a 2 port so you can’t service it wants ripping out and starting again
Thanks, could you clarify which bit you are referring to - so that I know exactly what I will be referring to when go back to them (and perhaps Gas Safe to make sure they were G3 qualified). Thanks for your input.
 
D1 is rising
T and p has been altered from manufacturers spec
No tundish
D1 is too long
D2 is incorrectly sized
2 port is inaccessible
Pump is inaccessible

just to name a few
 
Thanks, could you clarify which bit you are referring to - so that I know exactly what I will be referring to when go back to them (and perhaps Gas Safe to make sure they were G3 qualified). Thanks for your input.

As much as you don't want hear it my friend almost everything in the picture from what I can see is non compliant, or against standard procedure.
 
D1 is rising
T and p has been altered from manufacturers spec
No tundish
D1 is too long
D2 is incorrectly sized
2 port is inaccessible
Pump is inaccessible

just to name a few
When you refer to D1 and D2 - what does that mean? I think you are referring to the pipes from the valve but is the "D" for down? Thanks.

There's one other thing - they didnt remove the carpet in the airing cupboard when they changed the cylinder - so now the cylinder sits unevenly - part on the carpet and part off (due to the difference in cylinder sizes). You would have thought they could see that when they put it on!
 
Last edited:
When you refer to D1 and D2 - what does that mean? I think you are referring to the pipes from the valve but is the "D" for down? Thanks.

the pipe from the valve that they changed

1621455135500.gif
 
Hi, In terms of registering the work with building control how does that work? Is the installer meant to notify the council? How quickly will it show up with the council so that I can check they met the G3 requirements? Thanks for your input.
 

Reply to Solar Thermal Cylinder Installation in the Renewables area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
339
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
245
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock