W

Wintersun

Hi all,

my 1st post here! I have searched all over the net and can't really find an answer to my quest!

I have a Potterton Netaheat Profile 40e boiler, controlled by a Potterton Ep2001 timer.

I currently do not have a room thermostat in my house. But would like one fitted to my living room.

I have seen youtube video showing how to wire up a wireless thermostat to "a" boiler. Im pretty good with electrics so im sure I can install one, but.....

The problem Im having is, can a room thermostat be fitted to my Potterton netaheat profile 40e? or EP2001 timer controls?

I basically need to know where the wires go!

Also if I have a thermostat fitted, what do I do with the original timer controls? Keep them in place and have them set to constant and let the thermostat control it?

I have a fully pumped heating system. So I believe that would be diagram H on page 3 of the manual?

My timer control diagram
[DLMURL]http://www.gtts.co.uk/EP2001/PottertonEP2001InstallerGuide.pdf[/DLMURL]

My Wireless receiver diagram
http://www.free-instruction-manuals.com/pdf/p4766387.pdf

What wires from the wireless receiver would I tap into on the timer or the boiler?

My timer panel opened. (reads A B C D L N 1 2 3 4 5)
photo.jpg

My wireless thermostat receiver opened.
photo2.jpg

Thanks

Matt
 
Last edited by a moderator:
Hi Wintersun,

The work you are wanting to do is controlled work under Part P of the building regulations so you would be much cheaper getting an electrician in (who is registered with a competent person scheme such as NICEIC) to do it for you than paying the local building inspector to come out and give you the certificate you will need when you sell your house.

Not notifying building control on this work is illegal (either through a competent person scheme or by notifying them yourself prior to doing the work) so don't take the chance, they will catch up with you when you sell your home.
 
Last edited:
Well blow me!!! I'm carrying out illegal work :) I thought Part P was for upto the fuse spur? So are you saying crOft that if i change a room stat or wire in a room stat, something I've done for 30yrs, I'm carrying this work out illegaly? Honestly that's the first I've heard!!
 
wintersun ... bye the way, it'd not cost you much to get a GSR guy, NOT PART P, like myself to sort it for you no bother :)

Is the white wire into '4' on the programmer back plate from the diverter valve actuator?
 
cheers for the replys guys :)

I could get an electrician in to do the work, but why would they sell these items in diy stores if you then need to call a specialist in to do it for you?

Someone must know which 3 wires I need to connect to the stat receiver from the timer control panel?
 
Live, Neutral and switched live are the 3 wires wintersun ... if you're using 3 wires though you'll need a link in the sender :) Reason I asked about the white wire is that it's important to know its destination also :)
 
Hi diamondgas,

the white wire in 4 is indeed to the actuator valve.

Which wire goes from the timer panel (A B C D L N 1 2 3 4 5) onto L, N , L1, LX, L2 on the wireless sender? What link will I need on the sender?

thanks

photo3.jpg
 
Last edited by a moderator:
Okay seeing as it's Christmas and you'll probably find out somewhere down the line :)

L - L
N - N
L1 - C
remove white from 4 and put in in C

Link L to LX in the sender :)

Now it doesn't matter if you have your programmer on or off for central heating. The heating demand has been bi-passed to the extremly crappy RF stat you've bought :rofl:
 
Last edited by a moderator:
So if I set my CH timer to off and turn the Stat up to above the room temp, the boiler will click in and fire up?

I can still use the timer controls to control my HW as before?

What RF Stat would you recommend? nothing too expensive, but one thats good and does the job I want it to do.
 
Last edited by a moderator:
Thank! :hurray: Whats wrong with my RF stat??? :prrr:

Changed a good few in my time coz they just stop working after a year or two!!! They may have ironed out the glitch by now, I know they've had at least 2 versions so far, but I stay clear of siemens RF coz of past experience :)
 
So if I set my CH timer to off and turn the Stat up to above the room temp, the boiler will click in and fire up?

I can still use the timer controls to control my HW as before?

Now it gets complicated Wintersun! You'll always get hot water BUT it depends on how the rest of the system is wired as to whether you can have heating indipendantly if the programmer is "off" on hot water!
 
Now it gets complicated Wintersun! You'll always get hot water BUT it depends on how the rest of the system is wired as to whether you can have heating indipendantly if the programmer is "off" on hot water!

I've only been in this house a year and as far as I can work out, the CH and HW can be run separately on the potterton EP2001 timer thats currently wired up to my system. My HW is mostly off all day apart from 2 hours in the morning. But the CH works fine with the HW off on the timer.
 
Last edited by a moderator:
Status
Not open for further replies.

Reply to Wiring in room stat to my Potterton Netaheat Profile 40e in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock