Sarie

Hey guys, I'm sure this comes up a lot but I was hoping someone could help me out.

I recently bought a new house with a Baxi Bermuda 401 back boiler in the lounge and an old gas fire over the front of it. I was surprised to find that the ventilation was located in the kitchen with no vents through from the lounge to the kitchen but the previous owner provided a certificate and said her son was a gas safety engineer and had certified it safe before the sale. I've been leaving the kitchen/lounge door wide open and have rammed a door stop under it as I'm not happy at all. From checking online the maximum output from the boiler is 11.70kW but I'm not sure what the output of the fire is. It's an outset gas fire so I'd guess somewhere in the region of 6kW but I'm not sure.

Anyhoo.. I'm having external solid wall insulation fitted in a few weeks and as part of the scheme a gas engineer came out to check everything prior to the work being done. I discussed ventilation with him and pointed out that it was in the wrong room and he was surprised it had ever been signed off. He said the boiler was classed as "At Risk" and he wanted to turn it off. Given that the work on the house is being done in a fortnight (this will include rectifying the issue with the ventilation) and it's -4c overnight right now we agreed that I'd sign a disclaimer to prevent him from turning off my boiler for now as it would leave me with no heating or hot water, not ideal at this time of year. He's actually the one who'll be doing the work to fit the new vents in a couple of weeks anyway and as I have two CO meters and have jammed the kitchen door open he agreed to let me sign the disclaimer and keep the boiler on until he comes out to fit the new vents in a couple of week's time.

I know that in order to be safe I'm going to be stuck with large and draughty vents in my living room once the works are complete but I just wanted to know if there are any vent baffles or covers that meet regulations to divert the draught at all once the ventilation is fitted? I know you can get cowls for external wall vents to prevent wind blowing directly into the house but I've no idea if these are safe/legal or not?
The current setup in my kitchen right now is two 20cm vents, one high and one low. Both just have a bit of mesh stuck over them so you can see straight outside and when it's windy it blows a full on gale into the kitchen. My understanding of gas regs isn't great (thus me taking advice from the experts) but, from what I can grasp, the new vents are going to need to be bigger to meet regulations so it's going to be pretty chilly in my lounge. Makes the external wall insulation I'm having done a bit pointless really lol. If only I had £3k for a new boiler!

I'll try to get the ventilation fitted somewhere in the lounge where it's not going to freeze me and I wholly understand the necessity for the ventilation in order to ensure the boiler burns properly and doesn't kill me, but any advice on ventilationand minimising cold would be appreciated as I'd rather know what I can and can't have done before the work starts than after it's done :)

Thanks in advance!

Sarah
 
Hi Sarie, is room solid floor? You could duct under the floorboards if that's possible. Otherwise get the vent fitted as close to the boiler as possible. There'll be a draught from the vent to the fire for sure!

Did the engineer who called not suggest anything to you? Seems weird they didn't!
 
Last edited by a moderator:
If you google stadium vents you will find some with internal baffles that cut the draught but don't cut the air flow, (BM72 springs to mind, not sure if that's the right code or not) I would take the last engineer to task over him signing it off as safe, I assume he took his mums side rather than the correct action, and it makes me think the safety check he didn't wasn't the best, you could consider asking Gas Safe to investigations his competence if you make a complaint about him, it's not good enough to sign these things off of they aren't correct

BM 418 IS THE VENT YOU NEED
 
Last edited by a moderator:
There are loads of houses have the ventilation into the floor boards depending on room and airflow, normally your solum will be ventilated to the outside which can give great airflow,
 
Are you sure no vent louvres/ducts are in an obscure location or on the very bottom edge of the interconnecting door(s).
No chance theyve been wallpapered over inadvertently. ???

Cant understand why someone would go to the trouble of fitting external vents and ommiting internal.

If there's any - internal should be sited 450mm or lower.
 
Last edited by a moderator:
The installation is AT RISK disclaimer or not. As kirk says a stadium Black hole vent has baffles in it to reduce drafts, but must be in the room where the appliance is situated. The existing ventilation in the kitchen I not suitable because it is not big enough, has fly screens and does not have a clear passage to the lounge. Long term, look at a modern day efficient boiler.
 
Thanks for the replies everyone. Unfortunately I have a concrete floor downstairs so there's no option for underfloor vents in the house. The house is an old 1950's style poured concrete build.
I've checked several times and there are definitely no vents through to the kitchen but I have to wonder if there was even a kitchen door in place when the vents were initially fitted. The boiler is probably over 30 years old so I wouldn't be surprised if when it was fitted the current ventilation setup was deemed acceptable.. it certainly isn't now :)

The room is 10 ft wide by 20 ft long and the boiler is bang in the middle of the 20ft length with external walls at either end so unfortunately, no matter where I put the vent, it will be at least 5+ feet away due to the layout of the house. I'll ask the fitter about the BM418 vent, thank you so much! That would be far less draughty than the current arrangement.

I'm completely accepting of the fact that I have to have the vents and I know the result of that is that there'll be a draught and that's preferable to death. I'm just hoping to reduce the draughts when the boiler isn't operational if possible and prevent gales in the house on particularly windy days. I'm based in Scotland so there are plenty of those ;)

I'd love to get a modern day efficient boiler, but the current BBU works very well and there's nothing wrong with it. Having spoken with the gas engineer he suggested a conservative figure of £3k to upgrade to a modern boiler due to the placement of my existing boiler and that's without taking into account sorting out the fireplace after the BBU and outset fire are decomissioned so it's just not financially viable for me at the moment. The plan for now is to sort out the ventilation with the existing BBU and upgrade the heating controls (currently ancient rotary dials) and add a thermostat. I'm also going to get it all serviced as I don't trust the previous owner given they signed off on dodgy ventilation! I think that's the best I can do right now - money is a frustrating limitation sometimes.

Thanks again for all the advice!
 
Where abouts are you in Scotland? There are a few of us up here who might be able to help out with a decent quote, (not me, I'm in scotland but don't do any real work anymore haha)
 
Where abouts are you in Scotland? There are a few of us up here who might be able to help out with a decent quote, (not me, I'm in scotland but don't do any real work anymore haha)

I'm in Dalkeith, Midlothian - just south of Edinburgh :) The chap currently scheduled to do the work is doing it as part of the insulation work I'm having done - he's working with SERS. It's a big home energy scheme they're running up here at the moment so the majority of my street are having the external wall insulation done as we only have to pay 15% of the total bill to get it sorted so it's a ridiculously good deal!
Apparently the insulation will add an extra 5 inches to the depth of the walls so they're having to redo all the ventilation for people with BBUs as at the very least the vents need extending and apparently the situation with my poor ventilation isn't uncommon along the road so they're having to rectify quite a few. They did say that SERS may pick up the tab for the work and absorb it as part of the cost of the insulation works but if they won't then he's quoted me £100 inc VAT to put in the new vent but that's not including the cost of the stadium vent (assuming I can persuade him to fit it).
 
Status
Not open for further replies.

Reply to Ventilation in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have a 40 year old floor standing Glow Worm 45-60 boiler (open vent )which is in a cupboard in the centre of the house. Its an old workhouse...
Replies
2
Views
352
The soil pipe from my bathroom passes through the outside wall and into the roofspace above the adjacent single storey kitchen before dropping...
Replies
4
Views
144
We moved into a house with a gas Aga (I think converted from oil). The extraction pipe is fitted against and runs through an external wall, then...
Replies
4
Views
183
Hello - I have installed a garden sump-pump. In the photo you can see that I’ve replaced the Cloakroom-sink bend that previously went to the...
Replies
7
Views
562
I have a Remeha Tzerra M 24c Plus boiler. It is sitting nice and tight, next to the central ventilation unit/pipeline of the apartment block. That...
Replies
9
Views
851