Two loop UFH system heating 24M2 with lots of glass.
Loop lenghts 90M each X 16MM OD piping

UFH output 9.52kw.
flow/return 55C/34C, dT 21C
fowrates, 3.0LPM & 3.5LPM = 6.5LPM total

Boiler Vaillant Ecotec plus 438.
flow/return 65C/59C due to high recirc rate required to get the boiler away at ignition conditions with UFH only on.
The UfH output was "validated" by taking gas meter readings which gave a boiler consumption of 11.44kwh which gives a boiler efficiency of 83.2% so reckon reading reasonably accurate.

Query: Is the UFH output of 9.52kw from a two loop system and a dT of 21C plausible? and if so does it indicate that the heat is being dissipated in a badly installed under floor system.

1700663812931.png
 
Last edited:
You would get inconsistent floor temp eg hot spots and cold spots if you run it at a dt 20 ideally should be dt5-7 so floor heat around 2.2kw-3.1kw but as you need to increase the flow this will alter try doubling the flow and see what you get
 
If the flowtemp was reduced to a more "normal" say 40C what dT would you expect with the present flowrates, 3.0LPM&3.5LPM and loop lengths (90M) and OD (16mm).
 
The average pipe spacing is 24 m^2 / 90 m = 0.27 m so I'm guessing it's a 200 mm system with 18 m^2 of heated area. IIRC, the maximum output for the heated area should be around 100 W/m^2 (16 mm pipe, concrete screed floor, 200mm spacing). Downwards heat loss should be no more than about 10 W/m^2.

So, if I've understood/guessed correctly, with Tf–Tr = 21°C you are supplying an average of 395 W/m^2 to the room and 533 W/m^2 to the heated area. So, my guess is that the pipework layout was to be designed to operate at Tf – Tr = 4°C – 5°C and emit a total of 1.8 - 2.4 kW, i.e. not far from @Ben-gee's heat loss estimate.

What does your heat loss calculation for the room come up with?
 

Reply to UFH with high Output and high dT in the Water Underfloor Heating Advice area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
231
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock