J
Jayelem
I wanted to share some of my experiences with heating setup after I had a new boiler, controls and hot water cylinder fitted. The plumber who fitted it was, I think really experienced and capable, and worked hard (two men, two days) to finish off a very professional installation.
At switch-on, some radiators were a little cool, but after a quick balance, it was pronounced OK, and they left. Total cost for a Worcester 18Ri, cylinder, controller, thermostat, zone valve, tank stat., pump, Magnaclean and inhibitor was £3000. Expensive, but in line with other quotes I received. Overall, I was pleased.
Being an Engineer, though, I wasn't happy with the heat output; downstairs cooler than up, and one radiator particularly cold, whilst others boiled.
I wanted to balance the system properly, so I bought a non-contact IR thermometer (£12 from EBay) and this made the job very easy. I created a simple table of the temperature on both sides of each radiator, 10, 20, and 30 minutes after switch-on, and plotted a chart so I could see the results more easily. I also checked the top/bottom differential.
The first thing I did was look at the pump speed, as it seemed to be going very fast, and was a little noisy. Dropping it from 3 to 2 made little real effect, but 2 to 1 slowed the heat-up period, so I left it at 2.
Next, I balanced all the rads using my thermometer, and though this made a big improvement, the downstairs was still cooler. Conventional wisdom says downstairs cool is a pump fault, but with a new pump working OK, I knew this couldn't be right.
I then looked at the control system, and saw a manual bypass valve between flow and return. I have TRVs on all rads except the hall, where the thermostat is, so I figured I could close this down slightly to force more flow to the downstairs rads (I have a question on this, see below)
This made a massive difference, and the downstairs rads got much hotter, quicker.
Whilst I was there, I reasoned that the indirect coil on the cylinder is just another radiator, and also throttled this back via its manual valve in the return pipe.
The overall effect was astonishing, and the heating is now quicker, hotter and quieter. I did have some TRV whistling, but by opening the lockshield slightly, this went away (except on one occasion when a sharp tap on the valve body appeared to settle the jumper and stop the noise). Taking some flow from the cylinder and bypass has made all the difference.
The recommended pipe layout in the boiler installation notes shows two options; one with no bypass at all, and the other with an automatic bypass between flow and return. I believe that as I have one radiator without a TRV this will act as a bypass if all rads shut down and the cylinder valve is shut. Is this true? I didn't want to close down my manual bypass completely, so I just throttled it back a little, so the boiler can get its bypass via both the radiator and the bypass valve. Is this a good plan? I am not a plumber, but I think all the above is based on sound principles.
I guess I could work on the principle that if it's working it must be right, but I'm curious, so I'd appreciate any comments.
Doing this work wasn't difficult, but I guess you do need some understanding of heating systems, and a mechanical aptitude. I can understand and appreciate that a commercial plumber can't spend the hours I did, but conversely, had I been a little old lady, would I have had to put up with a very inefficient system? Where is the balance (no pun intended!) between profit and customer service?
At switch-on, some radiators were a little cool, but after a quick balance, it was pronounced OK, and they left. Total cost for a Worcester 18Ri, cylinder, controller, thermostat, zone valve, tank stat., pump, Magnaclean and inhibitor was £3000. Expensive, but in line with other quotes I received. Overall, I was pleased.
Being an Engineer, though, I wasn't happy with the heat output; downstairs cooler than up, and one radiator particularly cold, whilst others boiled.
I wanted to balance the system properly, so I bought a non-contact IR thermometer (£12 from EBay) and this made the job very easy. I created a simple table of the temperature on both sides of each radiator, 10, 20, and 30 minutes after switch-on, and plotted a chart so I could see the results more easily. I also checked the top/bottom differential.
The first thing I did was look at the pump speed, as it seemed to be going very fast, and was a little noisy. Dropping it from 3 to 2 made little real effect, but 2 to 1 slowed the heat-up period, so I left it at 2.
Next, I balanced all the rads using my thermometer, and though this made a big improvement, the downstairs was still cooler. Conventional wisdom says downstairs cool is a pump fault, but with a new pump working OK, I knew this couldn't be right.
I then looked at the control system, and saw a manual bypass valve between flow and return. I have TRVs on all rads except the hall, where the thermostat is, so I figured I could close this down slightly to force more flow to the downstairs rads (I have a question on this, see below)
This made a massive difference, and the downstairs rads got much hotter, quicker.
Whilst I was there, I reasoned that the indirect coil on the cylinder is just another radiator, and also throttled this back via its manual valve in the return pipe.
The overall effect was astonishing, and the heating is now quicker, hotter and quieter. I did have some TRV whistling, but by opening the lockshield slightly, this went away (except on one occasion when a sharp tap on the valve body appeared to settle the jumper and stop the noise). Taking some flow from the cylinder and bypass has made all the difference.
The recommended pipe layout in the boiler installation notes shows two options; one with no bypass at all, and the other with an automatic bypass between flow and return. I believe that as I have one radiator without a TRV this will act as a bypass if all rads shut down and the cylinder valve is shut. Is this true? I didn't want to close down my manual bypass completely, so I just throttled it back a little, so the boiler can get its bypass via both the radiator and the bypass valve. Is this a good plan? I am not a plumber, but I think all the above is based on sound principles.
I guess I could work on the principle that if it's working it must be right, but I'm curious, so I'd appreciate any comments.
Doing this work wasn't difficult, but I guess you do need some understanding of heating systems, and a mechanical aptitude. I can understand and appreciate that a commercial plumber can't spend the hours I did, but conversely, had I been a little old lady, would I have had to put up with a very inefficient system? Where is the balance (no pun intended!) between profit and customer service?