Discuss Rayburn 499k intermittent lockout. in the Central Heating Forum area at PlumbersForums.net

R

Ron Cole

This Rayburn 499k is serviced regularly. Individual components tested but goes into 'lock out'. It fires immediately when illuminated button pressed on control.
There is no pattern to when lockout occurs. It may be several times a day or several days.
Any ideas Anyone?
 
As above which burner. Have you managed to listen what the burner does and doesn’t do during the relight attempt before it goes to lockout?
 
The start sequence for pressure jet burners is around 15 seconds, depends on the type of control box. That is normal operation. Unfortunately intermittent faults are often the most frustrating because they don’t always reveal themselves when an engineer is present and 99% of homeowners don’t have the time to sit around waiting for it to happen and make notes.
I can’t say what the problem is as it could be a number of things. If you happened by chance to catch a video with sound of the burner when flame fails and it attempts to relight before lockout I might be able to point you in the right direction, although you could be sitting next to it for hours before it happens. Your best bet is to find an engineer to attend, preferably an engineer found on the Aga/Rayburn website.
 
The start sequence for pressure jet burners is around 15 seconds, depends on the type of control box. That is normal operation. Unfortunately intermittent faults are often the most frustrating because they don’t always reveal themselves when an engineer is present and 99% of homeowners don’t have the time to sit around waiting for it to happen and make notes.
I can’t say what the problem is as it could be a number of things. If you happened by chance to catch a video with sound of the burner when flame fails and it attempts to relight before lockout I might be able to point you in the right direction, although you could be sitting next to it for hours before it happens. Your best bet is to find an engineer to attend, preferably an engineer found on the Aga/Rayburn website.
First line of defense was Aga. NBG!! They don't know.
 
The problem is the 400 series of Rayburn have always been problem child’s. Engineer’s either know them well but don’t want to touch them or don’t know them at all.
 
If you could tell me the type of burners in them please. The 400 series have used several burners over the years. Also if I could have the area you live in I will see if I can find someone who covers your area and is prepared to have a look for you b
 
The problem is the 400 series of Rayburn have always been problem child’s. Engineer’s either know them well but don’t want to touch them or don’t know them at all.
I was heavily involved in the cooker market when the twin burner rayburn was introduced ( we were Stanley agents.)
It was brought out in a huge hurry to combat the twin burner Stanley that was outselling Rayburn by a distance.
The Rayburn was always a problem despite many changes / redesigns. The taisan oil pump oil pump a particular low!
 

Reply to Rayburn 499k intermittent lockout. in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
232
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
324
Hi, basic question, any insight much appreciated. Looking to have an outdoor tap in my front porch fed from 15mm pex coming up from suspended floor. Pic 1 is inside porch, pex temporarily clipped to give an idea of pipe placement (ignore shoddy blockwork of booted cowboy builder!), Pic 2 is...
Replies
6
Views
226
  • Sticky
Morning to any Australians lurking around! Register its free, then message me, I'll sort your account out for you. We will need a moderator from each main country too. I'll post this in the Australian forum now.
Replies
0
Views
77
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
245
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock