Hi

Can anyone help. I went to look at a Megaflow, last Saturday ( I have my unvented card) the client was saying that in the evenings, every two or three days the megaflow discharges hot water out of the discharge pipe.

It is a 210litre direct megaflow unvented cylinder

There was no leak coming through the tundish and the expansion and t and p valves. So I assumed that the air gap needs recharging. I followed the procedure in the installation manual ( when I held the t and p valve open there was alot of gurgling in the valve and this took about 5mins to clear.

However the client called me today to say that the megaflow discharged water earlier today.

Any thoughts anyone??

Thanks

Paul
 
u didnt make the air gap properly, it should only be air then water when u stop filling to the discharge point, fm the sound of it you may have just filled it too much
 
Hi Lame Plumber

Thanks for your reply, do you mean I let too much air in. Do you mean I should keep the t and p valve open only as long as water discharges through the lowest tap? Then the air gap will be recharged?

5 minutes until the gurgiling stops is a long time

Paul
 
Hi

The cylinder is downstairs and so are the taps. I called Megaflow and they advised me to drain down the tank from the inlet as this would allow the air gap to reinstate. As the taps are at the same level as the cylinder, this is the only way to do it.

I did this yesterday so hopefully problem solved

thanks

Paul
 
Hi

The cylinder is downstairs and so are the taps. I called Megaflow and they advised me to drain down the tank from the inlet as this would allow the air gap to reinstate. As the taps are at the same level as the cylinder, this is the only way to do it.

I did this yesterday so hopefully problem solved

thanks

Paul

did this work?
 
did this work?
Hi

Just to let you know, by draining down the tank, this worked and the problem is now solved. This is worth remembering as in the manual there is no mention of solving the air gap this way. It is worth remembering that if the lowest hot tap is on the same level as the megaflow the best thing to do is to drain the cylinder

thanks

Paul
 
Status
Not open for further replies.

Reply to Megaflow discharge problem in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock