Powerflushed a system yesterday with a 2 year old veissman vitodens installed on an old system with the twintec installed at the same time as the boiler.
customer complaing rads wernt getting and hot water running hot cold hot cold but boiler fireing upto 100 degrees!
Isolated boiler and flushed system.....while doing this took out plate which was full of magnatite and soaked in sea of salts....came out spanking new.
I then flushed through boiler to find couldnt get no circulation at all!! I then felt the rubber hose from the main heat exchanger to flow valve which was jammed pack with magnatite.....after squeezing the whole pipe i dislodged all thw magnatite and wallop.....the water flew around the boiler.....at the end i had a filter full of sludge and a very happy customer.....
But my verdict on the so called supirior twin tec is that its not fit for purpose and i wouldnt buy or fit one of these...would fit something else....i think my nans pants would have been a better filter!!!
Sent from my GT-I9100 using Tapatalk
customer complaing rads wernt getting and hot water running hot cold hot cold but boiler fireing upto 100 degrees!
Isolated boiler and flushed system.....while doing this took out plate which was full of magnatite and soaked in sea of salts....came out spanking new.
I then flushed through boiler to find couldnt get no circulation at all!! I then felt the rubber hose from the main heat exchanger to flow valve which was jammed pack with magnatite.....after squeezing the whole pipe i dislodged all thw magnatite and wallop.....the water flew around the boiler.....at the end i had a filter full of sludge and a very happy customer.....
But my verdict on the so called supirior twin tec is that its not fit for purpose and i wouldnt buy or fit one of these...would fit something else....i think my nans pants would have been a better filter!!!
Sent from my GT-I9100 using Tapatalk
Last edited by a moderator: