Discuss Isolating boiler to test if hex is causing pressure loss in the USA area at PlumbersForums.net

Matt0029

Gas Engineer
Messages
1,138
If Isolating a boiler to determine if the leak is on the pipework or the boiler. If pressurising to 1.5bar then isolating the flow and return for an overnight test. Is it still acceptable to use the combi boiler for hot water? Expansion vessel located in the boiler.
 
Yes fine to use hot water but it may invalidate your test if the expansion isn’t good enough eg over 3 bar etc
 

Reply to Isolating boiler to test if hex is causing pressure loss in the USA area at PlumbersForums.net