Hi. I have a firebird enviromax combi boiler. each time it turns off the motor on the riello burner keeps running for a while then the whole thing goes into lock out. flashing green and red.
shouldn't the motor turn off straight away? I'm also getting pressure building up while it's running but the expansion vessel had gone so a plumber fitted a new one away from the boiler but put it on the return side of the flow instead of on the actual flow side, I think that's why I'm getting high pressure but as for the motor still running after it's switched off and it's no longer giving a flame then going into lock out if anyone has any ideas I would really appreciate it
 
Yep, get your engineer back.

Recently serviced?

Photocell partially sooted? Which could mean flue or combustion issues.

Expansion vessel is best on return, less affected by high temperatures.

Why didnt they just fit a new one on the boiler, check its pressure and clean out connecting flexi.
 
Yep, get your engineer back.

Recently serviced?

Photocell partially sooted? Which could mean flue or combustion issues.

Expansion vessel is best on return, less affected by high temperatures.

Why didnt they just fit a new one on the boiler, check its pressure and clean out connecting flexi.
yea recently serviced but it was giving this problem before the service. new pressure vessel is about 10ft away from the boiler connected with 3/4 copper he left the old one connected to the boiler. the photo cell is clean too. I don't understand why the motor/ fan still runs after I've switched the boiler off at the timer control. runs for about 10 seconds or so then the lock out light next to timer controls comes on and restart button on the burner control box flashing red and green. I think the control box on the burner is different to the usual control boxes I've seen in the past. this one is a MO/535 I think?
 
Some low emission oil fired boilers now do a post purge after the burner shuts down, as well as the mandatory pre purge of 10 secs or so, this post purge obviously shouldn't flag a lockout. maybe worth having a word with Firebird.
I also think I read somewhere that this post purge can be switched off.

EV's are normally tied in at the pump suction but I see some gas fired (combi?) boilers have it to the pump discharge.
 
Some low emission oil fired boilers now do a post purge after the burner shuts down, as well as the mandatory pre purge of 10 secs or so, this post purge obviously shouldn't flag a lockout. maybe worth having a word with Firebird.
I also think I read somewhere that this post purge can be switched off.

EV's are normally tied in at the pump suction but I see some gas fired (combi?) boilers have it to the

Some low emission oil fired boilers now do a post purge after the burner shuts down, as well as the mandatory pre purge of 10 secs or so, this post purge obviously shouldn't flag a lockout. maybe worth having a word with Firebird.
I also think I read somewhere that this post purge can be switched off.

EV's are normally tied in at the pump suction but I see some gas fired (combi?) boilers have it to the pump discharge.
could it be a problem with the actual burner control unit? when the boiler controls go into lock out the restart button on the burner control flashes green and red.
 
the burner is a riello MO535 digital control box

Some low emission oil fired boilers now do a post purge after the burner shuts down, as well as the mandatory pre purge of 10 secs or so, this post purge obviously shouldn't flag a lockout. maybe worth having a word with Firebird.
I also think I read somewhere that this post purge can be switched off.

EV's are normally tied in at the pump suction but I see some gas fired (combi?) boilers have it to the pump discharge.
the boiler is about 10 years old, fitted in 2013. It's a indoor module. work that's been done so far to try and resolve the issue is a service, new expansion vessel but not the original type at the boiler. the plumber put it about 10ft away where the hot water tank used to be. when it was serviced the guy said he had to replace the fuel pump as he couldn't adjust the pressure to the nozzle and said there was a carbon monoxide issue. It also runs extremely hot ,doesn't seem to regulate the temperature, the burner doesn't cut out unless I actually turned it off so he then replaced the temperature control module. This wasn't cheap as it's a circuit board, he also changed the thermistor? one for the boiler, one for the hot water and a flow thermistor? but it still continuously runs until I switch it off. at this stage the pressure Guage reads 2.5bar I'm afraid to let it go any higher
 
You need to bin off your oil engineer and get somebody in who knows what they are doing rather than just chucking parts at it.
I hear you loud and clear. unfortunately I live in a very remote part of Ireland and can't get a definite day from anyone else to look at it and with the cold weather now set in and new born baby in the house I'm desperate, hence trying to get some answers here
 
You seem to have 2 problems here.
Combustion problem, a indoor model will take he air for combustion from outside, you might see a small hole in the wall underneath or above where the exhaust leaves the building, can you trace these and post a photo of your boiler front?. The combustion gases may be short circuiting the air somewhere, maybe at the boiler.

EV problem, what is the vol of the EV and how may rads have you got?
 
You seem to have 2 problems here.
Combustion problem, a indoor model will take he air for combustion from outside, you might see a small hole in the wall underneath or above where the exhaust leaves the building, can you trace these and post a photo of your boiler front?. The combustion gases may be short circuiting the air somewhere, maybe at the boiler.

EV problem, what is the vol of the EV and how may rads have you got?
I'm out at the moment but I'll put up a photo and video if possible later today. The EV is a 18ltr and there's 23 radiators on the system
 
The 18L, with precharge/filling pressures of 1.0bar/1.5bar will sufficient for a130L system with a hot pressure of 2.0bar, 190L at 2.3bar and 220L at 2.5bar.

I will PM you a well known Irish site which should recommend a good service person in your neck of the woods.

PM sent.
 
The 18L, with precharge/filling pressures of 1.0bar/1.5bar will sufficient for a130L system with a hot pressure of 2.0bar, 190L at 2.3bar and 220L at 2.5bar.

I will PM you a well known Irish site which should recommend a good service person in your neck of the woods.

PM sent.
Thank you John, very much appreciated 👍
 
Thank you John, very much appreciated 👍
finally got this sorted. actually did it myself. error code of green and red flashing light indicates extraneous light but this was only happening on the post purge causing the burner to lock out. I checked the burner that was just service a couple of weeks ago. I could see that the electrodes were arcking to the nozzle instead of each other so I adjusted the gap and tried again, still the same so I replaced the photocell and hey presto no lock out.
I won't be getting the same guy back for the next service anyway. Appreciate the help and suggestions lads 👍
 
finally got this sorted. actually did it myself. error code of green and red flashing light indicates extraneous light but this was only happening on the post purge causing the burner to lock out. I checked the burner that was just service a couple of weeks ago. I could see that the electrodes were arcking to the nozzle instead of each other so I adjusted the gap and tried again, still the same so I replaced the photocell and hey presto no lock out.
I won't be getting the same guy back for the next service anyway. Appreciate the help and suggestions lads 👍
Hi John, I hope you don't mind me messaging you directly. apologies in advance if you do. I'm just wondering about the nozzle that was fitted when the boiler was serviced. I'm running 23 radiators various sizes of course but I downloaded a manual for the boiler and the suggested nozzle for 31kw is a 0.85/80 ES but he fitted a 0.85/80 EH Could this be causing the burner to use more kerosene than it should?
 
Hi Dave,
I don,t think it will cause it to use more fuel, its probably just the spray pattern that's different although I suppose its best to keep to Firebirds recommended nozzle.

John.
 
Have a read of this Dave, or anyone else,you may find it interesting, I'm the one with the 16/17/year old Firebird that has never tripped on combustion failure in all this time, what a burner, a Riello G5X.

Thought I was PMing you!!.

Edit: I've removed this link and PMd you as I don't think its allowed on here.
 
Last edited:
Have a read of this Dave, or anyone else,you may find it interesting, I'm the one with the 16/17/year old Firebird that has never tripped on combustion failure in all this time, what a burner, a Riello G5X.

Thought I was PMing you!!.

Edit: I've removed this link and PMd you as I don't think its allowed on here.
lots of information there 👍
especially regarding nozzles and pump pressure settings. from what I could see regarding the older boilers an average of 85% efficiency is pretty much as good as it gets?
 
lots of information there 👍
especially regarding nozzles and pump pressure settings. from what I could see regarding the older boilers an average of 85% efficiency is pretty much as good as it gets?
Yes, that about the size of it, my 17 year old 20kw SE Firebird still runs with the same flue gas temperature as when new of 230/250C, gives around 83% efficiency, condensing loss of ~6% (for oil) + 11% flue gas loss).
 

Reply to firebird enviromax combi lock out in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
4
Views
390
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
310
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
234
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock