The utilities company say its the house owners job to have the cold water mains pipework upgraded i.e they're responsible upto the property boundary wall.

Does anyone know what it would cost?

You will need to get someone in to give you a price as there are so many variables, hand dug, moled, type of ground to cross etc.
The pipe is laid from your boundary to the stopcock position.
The utilities company will give you a new connection for free and connect to the pipe at the boundary.
 
Yes, anything from inside the garden wall to the property stopcock and further into the property I'd have to replace.
Big job as I'd have to dig the front garden up. I dont want to do that.
May be better to just replace the internal mains water pipe from the stopcock. The stopcock is at the front door area. The kitchen / bathroom are at the rear.
 
Get rid of the lead mains pipe. Have it decided on the best place for new stopcock position inside the house and straight route to boundary and have it dug up. Or get someone with a mole to do any parts that you don't want dug up, or that are impossible without.
Most important pipe in your property is the water mains
 
Yes, anything from inside the garden wall to the property stopcock and further into the property I'd have to replace.
Big job as I'd have to dig the front garden up. I dont want to do that.
May be better to just replace the internal mains water pipe from the stopcock. The stopcock is at the front door area. The kitchen / bathroom are at the rear.

You can get it moled without having to dig too much. It doesn't cost anymore than digging it unless you can get someone from the pub to dig it for 50 quid.
Dig a hole at the boundary, one at the wall of the house, one every change of direction and if you are unlucky maybe maybe another hole or 2.
It is stupidity to leave the old lead in.
Would you still run around in a cortina? Bet yer next car to that cost more than your home comforts will.
 
Got to be careful the gas mains and electricity and water all come into the house along the same path. The gas meter, electric meter and water mains stopcock are in the front door area. And sods law its all lead pipes!!
So paying some chimp from the pub to play 'bob the builder' to dig a hole or two for ÂŁ50, no chance.
I'l make inquiries into having it moled out.
 
The boiler is in the fireplace and the external grundfos pump is situated sub floor by the side of the fireplace.
I have a couple of questions to ask. I drained the system down and removed a few radiators to flush the black sludge out. (there was quite a bit). Refitted, refilled and rebled radiators. The horstmann c27 timer started its program and the HW / CH worked ok. However the day after, there was only HW working , no CH. The programmer controls HW / CH at the same time, you cant select one or the other.
So I drained the system again, refilled, rebled the radiators and the HW / CH worked again. Day after no CH only HW in the cylinder tank. Both plastic feed and header tanks in loft both fill correctly.
I appreciate its an old system and it will be getting changed in the near future.
I also notice that when the boiler is off and the programmer is off. The boiler fires up on its own.
Can anyone shed any light as to why the system works for a day, then doesnt the day after?
There are no zone valves anywhere on this system either.
 
Turns out the wiring from the external pump and the boiler wiring to a junction box was incorrectly wired. Resulting in all wiring from the junction box to the external wall programmer was totally wired wrong, so when the boiler fired up for CH & HW the pump wasn't wired to run.
Looks like it'd been like this from original install. Corrected it iaw wiring diagram, all working properly now.
Took everyones advice and gone for a moled replacement mdpe pipe.
Thanks for all replies.
 
Turns out the wiring from the external pump and the boiler wiring to a junction box was incorrectly wired. Resulting in all wiring from the junction box to the external wall programmer was totally wired wrong, so when the boiler fired up for CH & HW the pump wasn't wired to run.
Looks like it'd been like this from original install. Corrected it iaw wiring diagram, all working properly now.
Took everyones advice and gone for a moled replacement mdpe pipe.
Thanks for all replies.
 
Status
Not open for further replies.

Reply to 1 or 2 pipe central heating system diagram in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
283
PSxxxxxx
P
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
444

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock