Condensation is the change of the state of matter from the gas phase into the liquid phase, and is the reverse of vaporization. The word most often refers to the water cycle. It can also be defined as the change in the state of water vapor to liquid water when in contact with a liquid or solid surface or cloud condensation nuclei within the atmosphere. When the transition happens from the gaseous phase into the solid phase directly, the change is called deposition.

View More On Wikipedia.org
  1. S

    Glow worm betacom 24

    What a terrible design on the condense trap! Anybody else experienced this?
  2. X

    Hi guys, please save me the time of researching

    Combi install to do, middle of bungalow. Condense pump needed. Running condense into pump like usual, but can this be teed off to a tundish for blow off or not. I would like to think you could but never done one. If you can tell me any other special requirements needed. Much appreciated lads if...
  3. R

    Dissolving condense pipe

    Was called called to a job today. Boilers been in for 2 years. The complaint was leaking condense pipe. I assumed it would be customer damage but when I looked at the elbows on the condense run they were all started to split and wrinkle. Normal overflow elbows. Never seen this before. Just...
  4. W

    condensafe!?

    i over heard a couple of gas fitters in my local merchants discussing condensafe fittings and from what i gathered they where basicly saying by putting one of these condensafe fittings on you can run the condense line to a rain water pipe? is this right or have i over heard a couple of liars?
  5. P

    Heat line 28E condense

    I am trying to find a replacement inner door seal for the above boiler, but no one seems to stock it. Part number for the door is 3003200064, but this isnt recognised !!! is there a generic type of seal i can use for this boiler, it is the spongy strip type ( if that makes sense!) boiler GC 47...
  6. B

    boiler blow off

    been called to a boiler today as british gas did an ID on it as it was on a contract and been passed by them each year till now .It was an older boiler i have never heard of its about 6years old - its in a terrace between the kitchen and bathroom and has no external walls , the condense goes...
  7. J

    Safety relief valve pipe

    Can I run the ‘safety relief valve’ copper discharge pipe into the plastic condencesate drain pipe? The boiler is a ‘Ideal - isar
  8. T

    washing machine into same pipe as boiler condense.

    Hi, I have a quick question regarding plumbing in a Washing machine. Our boiler is mounted on the wall above the space the washing machine will go into. Thanks to the previous tennants wrecking the boiler we had to have all the piping replaced underneath so now the condense comes straight...
  9. P

    acidic condense !!

    just did a cp12 on a keyston 60 its 3 years old the flue has been dripping and this is the result !! wow eaten bricks
  10. K

    condense pumps!!

    problem,, installed a boiler 2 years ago all working fine however the condense pump keeps freezing. the boiler is suitated in an outhouse and so is the condense pump, i have lagged the pipe itself that is not freezing the water inside the pump is causing havoc said i will try to solve this...
  11. S

    connecting condense to square downpipe

    Could somebody tell me the best method of connecting condense to square downpipe? Is there an adapter or is it just a case of drilling a hole with a speedbit? Thanks for any answers
  12. S

    Frozen condense

    Hi all How do you thaw these, boil kettle and pour it down flue?
  13. S

    Nice condense install

    Saw this on the way home....:eek: For you newbees this is how not to install a condensate..
  14. G

    Noisy Condense Pump

    I have just had a Worcester FS30CDi fitted which seems to be fine except for a fairly loud buzzing/vibration noise shortly after starting up. I guess this is from the condense pump, it lasts for about a minute at a time and is very noticeable because the boiler is otherwise pretty silent. Is...
  15. J

    Outlet for condense water - this legit?

    I live in flat so the big issue I am having is figuring out where to run the condense pipe, so far everyone wants to run a long pipe to the bathroom which will look ugly. Had one engineer today who said just run it outside, I am top flat and the side wall faces trees so wont affect anyone...
  16. J

    Boiler - Condense Pipe Issue

    Looking to change my boiler but the heating engineers are having issues figuring out where to run the condense pipe. I was told there might be an energy efficient boiler that somehow doesnt need a condense pipe - is this true - anyone know of make / model? Thanks
  17. L

    combined discharge and condense

    fitting some ATAG combis which have combined discharge and condense will condense pipe be ample for the heat in the event of a discharge
  18. G

    On-Call (frozen condense)

    oh dear! what a week on-call! Have had the busiest week ever with loads of burst pipes and have had to help out with boiler breakdowns. Now every frozen condense pipe ive done this week is from the Worcester Greenstar range. 22mm frozen, 1 1/4 frozen all different lengths (its been quite...
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock