I converted mine about 20 years back. Old cast iron floorstanding boiler, gravity HW, pump next to boiler, pumping downwards. No controls. Cold feed to boiler return.
Scrapped the boiler and installed wall-mounted condensing. Moved the pump to the airing cupboard, added diverter valve (system W), open vent, cold feed and DV in the airing cupboard. Added cylinder and room stats. Re-used the gravity 28mm pipes as pump suction and cylinder return.
Still working OK.

That is exactly what system I have to work on! :)
Cast iron oil boiler with 28mm gravities to cylinder and 28mm pumped (pump is also on return pipe) to rads. No controls.
The feed pipe joins in at tee at return at cylinder.
Your new pipe up arrangement would be nearly what I would ideally do, but difficult on this house. I might risk trying to seal the system - but at a low charge.
As to Vee’s point about sealing the system using gravity feed from f&e tank and non return valve, - I have came across systems done that way, some of which are fed from the cwt cold supply.
Personally I don’t like it because risk of contaminating cwt, also disadvantage that the sealed system will keep being topped up in an event of a bad leak, like nail through a pipe. Although constant top up has also advantages.
 
That is exactly what system I have to work on! :)
Cast iron oil boiler with 28mm gravities to cylinder and 28mm pumped (pump is also on return pipe) to rads. No controls.
The feed pipe joins in at tee at return at cylinder.
Your new pipe up arrangement would be nearly what I would ideally do, but difficult on this house. I might risk trying to seal the system - but at a low charge.
As to Vee’s point about sealing the system using gravity feed from f&e tank and non return valve, - I have came across systems done that way, some of which are fed from the cwt cold supply.
Personally I don’t like it because risk of contaminating cwt, also disadvantage that the sealed system will keep being topped up in an event of a bad leak, like nail through a pipe. Although constant top up has also advantages.
In my case the F/E tank is almost directly above the airing cupboard, so open vent and cold fill no problem. I chased the wall in the hall for the roomstat, and it was fiddly getting the lead through to the airing cupboard. Eberle roomstat, because it was cheap, but no complaints, has anticipator heater and gives excellent control. I guess you'll use a radio-controlled roomstat so won't have the cabling problem.
There is a common heating flow pipe not far from the airing cupboard so I ran a pipe under the floorboards and tee'd into that with CH flow from the DV.
 
My very scientific experiment :D

34" of head
1" single check valve
22mm feed
1 Williams f and e tank :D

Result

It works brilliant

IMG_3675.JPG


IMG_3676.JPG
 
Didn't think there was going to be enough head to open the check valve
With the suggested scheme the valve needs to close to prevent upward flow, if I understand correctly. Does it have a spring-loaded flap? Unlikely it will close otherwise. Or maybe use 2 90° bends so the valve is in a horizontal section, if it's the right type of valve. Or maybe 2 return bends so it's vertically down, but that gets a bit messy.
 
That's looks like low-head check valve. Am I right?

dont have a clue, bought the check valve on the designed i liked the most :D
 
With the suggested scheme the valve needs to close to prevent upward flow, if I understand correctly. Does it have a spring-loaded flap? Unlikely it will close otherwise. Or maybe use 2 90° bends so the valve is in a horizontal section, if it's the right type of valve. Or maybe 2 return bends so it's vertically down, but that gets a bit messy.

yes its spring loaded in the closed position
 
Status
Not open for further replies.

Reply to Feed and Vent fun :DDDDD in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Copper pipes, I think its fair to say, is not what it used to be, the copper is getting thin while the cost is going up. Meanwhile, plastic...
Replies
2
Views
323
S
Hi, I seemed to have a blockage in kitchen sink. A plumber came and cleared all the pipework that is visible inside my home (there was debris and...
Replies
2
Views
163
Sonya K
S
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
465
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m...
Replies
6
Views
326
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock