Aren't there two boards for these? A seven an a five wire?

I tell you what it's not like swapping a board on an isar when changing these, not a straight swap by any means
 
Aren't there two boards for these? A seven an a five wire?

I tell you what it's not like swapping a board on an isar when changing these, not a straight swap by any means


yes single or double fuse i dont mind changing them fiddly but easy.
 
I replaced a faulty PCb on a glowworm ultimate once as it was dead, it then only got to the sparking stage & I thought the new pcb was a duff but it was the pilot injector absolutely blocked solid.... Little wire brush managed to clear it & was okay since!

This one hadn't been serviced with big pile sediment over burners etc
 
Just to update you all :)

I went back to this one yesterday and followed all the advice, but to no avail.
After following the fault finder in the MI I have determined that the air pressure switch has given up.
There was gas at the pilot, but the pilot doesn't light. I checked the gas with my Honeywell sniffer btw.
There's a good spark, and as the boiler is sparking away I checked voltage at the APS only to find that I didn't have 230v so I'm presuming that its the APS at fault.

Just two queries though:

If the fan isn't working at full speed can this cause a problem with the APS?
I ask because the fan is making a grating noise but it is running.

Is the Ultimate 50FF fan the same as the Micron 50FF fan? There appears to be a huge difference in the price for the two and yet they appear to be the same, looking at the images I can find.
 
If it's sparking and gas is there it is not the pressure switch !
Is the spark in the right place and 2-4 mm from strike surface, have you filed or Emery papered it clean ?
 
Last edited:
I still think pilot blockage !
Gas may be there but not enough.
Change pilot and electrode !

That's what I would be doing
 
new pilot injector the holes are tiny in these it doesnt take much to block them
 
If the fan isn't working at full speed can this cause a problem with the APS?
I ask because the fan is making a grating noise but it is running.

Is the Ultimate 50FF fan the same as the Micron 50FF fan? There appears to be a huge difference in the price for the two and yet they appear to be the same, looking at the images I can find.
 
If its sparking then the fan and APS switch are working
 
fans do get noisy but it is operating the aps otherwise it wouldnt spark

1 call for heat
2 aps proves
3 spark
4 pilot solenoid open
6 pilot lights and proves with ionisation
7 main solenoid opens

you are getting to 4 so it has to be gas related (or spark is not enough to ignite ) you can prove this.
 
Status
Not open for further replies.

Reply to Gloworm Ultimate 50ff in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two...
Replies
2
Views
218
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about...
Replies
7
Views
257
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
554

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock