I have 2 lpg gas bottles outside the barn with new combi boiler inside.
my entire plumbing inside the cottage is now redone in plastic apart from feeds to the boiler.
the boiler is close to a sink
Can anyone suggest what earthing I will require and is any earth bonding required under the boiler?
Can I connect into an under counter earth terminal within a double socket which goes directly back to the CU and if so would an RCD socket be a safer option?
Or can I put in a new copper earth rod just outside near the bottles and connect a second earth to some part of the gas or water feeds ?
not sure if you can have 2 earth rods feeding the same property ?
many thanks in advance
 
The lpg will need everything as it enters the property as it's an incoming service.

@Murdoch

Equipotential bonding, to give the proper term , means that all services are connected back to the MET or fuseboard.

An external earth rod would not be suitable, nor would connecting it to a random socket.

If in doubt, I would recommend you consult a local spark

Hope this helps
 
Equipotential bonding, to give the proper term , means that all services are connected back to the MET or fuseboard.

An external earth rod would not be suitable, nor would connecting it to a random socket.

If in doubt, I would recommend you consult a local spark

Hope this helps
Thanks Simon- I was just elsewhere informed that the gas bottles are not classed as an external service - they have rubber pigtails connecting to the regulator isolating them from gas feed and in turn the boiler and the rest of the house electrical earth system - is this not correct? should I therefore just bond all the underside of the boiler terminals inc the gas pipe?
 
Equipotential bonding, to give the proper term , means that all services are connected back to the MET or fuseboard.

An external earth rod would not be suitable, nor would connecting it to a random socket.

If in doubt, I would recommend you consult a local spark

Hope this helps

Apologies, hit the dislike rather than like. Amended.
[automerge]1577104467[/automerge]
Thanks Simon- I was just elsewhere informed that the gas bottles are not classed as an external service - they have rubber pigtails connecting to the regulator isolating them from gas feed and in turn the boiler and the rest of the house electrical earth system - is this not correct? should I therefore just bond all the underside of the boiler terminals inc the gas pipe?

Earth bonding is all about your safety.
I'd go with Murdochs advice above.
 

Reply to Earthing requirements for combi boiler linked to LPG bottles. in the USA area at PlumbersForums.net

Similar plumbing topics

We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...