Search the forum,

Discuss False call for hot water in the Central Heating Forum area at PlumbersForums.net

tod

Messages
10
Good day

I’ve had three heating engineers look at the symptoms that follow to no avail. One of them replaced the electrodes ( part 5110992 )

Boiler: Potterton Promax HE Plus (SL) (2008)
Hot water tank: Heatrae Sadia Megatech Solar 190 Indirect (2008)
Thermostat: Nest 3rd Gen (2017)

Symptoms: (this started in December 2018 with no obvious trigger) an example from this morning, the hot water schedule turns on at 07:00 at which point the boiler turned on and did it’s thing for about 20 minutes. No hot water was used for the next 90 minutes. The call for hot water came in again and the following took place for the next 15 minutes:
The boiler goes through its startup routine, flame comes on, 5 second later it cuts off. Rinse and repeat for 10x+ iterations before it finally stayed on for 2 minutes after which the call for hot water disappeared.
No lights come on the PCB at the time of cut off to suggest there’s anything wrong.
the behaviour isn’t unique to hot water but with hot water this false start routine happens almost always. With heating it happens about 10% of the time.
The PCB was replaced April 2017. No other work happened between that and the electrodes being replaced.
As I said I had three heating engineers looking at it no avail. A lot of shrugging and head scratching turns into a phone call to a colleague but nothing comes out of it.
one heating engineer checked the resistance on the PCB and stated that electrically it is in order. That same engineer suggested that it’s a faulty gas valve inside the boiler(?) that displays the symptoms when the boiler is cold. That sounded odd considering heating does not trigger such behaviour as much as hot water but I don’t know anymore.

Any help would be truly appreciated as hearing the boiler fail to stay on is driving me mad on a daily basis. Thank you.
 
Any help would be truly appreciated as hearing the boiler fail to stay on is driving me mad on a daily basis. Thank you.
Check the simple things first.

Is the tank thermostat in the correct location and firmly strapped to the tank? If it gets loose, so the thermal contact is poor, or if it is set significantly higher than 60°C, you can get the symptoms you describe.

Measure the actual temperature of the hot water in the tank. (Use a thermometer and continously run a hot tap near the tank into a mug.)
 
Will do that once I acquire a thermometer, thanks for the advice.
A couple of points to add: the symptoms aren’t limited to when the call for hot water is false. For example now the call for hot water is genuine as it was off all day and we used hot water but it’s been cycling through the startup routine for 20+ minutes before finally staying on.
Also, when the boiler cuts off the call for heat does not, ie the motorised valve stays open near the tank and the pump stays running.
 
If the boiler is cutting out, whilst you still have an external call for heat, you really need a decent gas engineer ( who is familiar with the Promax HE ) to trouble shoot for you. It is not too difficult, they ( the Promax range )are very logical in how they perform.

Alternatively, try to get a fixed priced repair from Potterton.

I would doubt that this is a difficult fix, but it is not a DIY repair. Apologies but I cannot say more.
 
Thank you both.
I do have heating breakdown cover with no excess so I could keep getting them out but it’s just a nuisance. Posts on DYINOT suggest it is a pretty common fault with this model however their boilers normally result in ignition lockout which mine never does. One evening it kept trying to light for over an hour.

My ranting aside, at what point does one justify getting a new boiler instead of trying to repair a 10+ year old Potterton? Clearly it’s still got life in it as it’s been doing this for a year now but it would be good to know if that’s it signalling me that it’s on its way out and I should send Santa a letter changing what I’ve wished for.
 
I don’t think that your boiler is “on the way out” - but you do need to decent gas safe registered technician to resolve the issue for you.

The fact that the boiler does not lock out, narrows the issue down to the root cause(s) - non of which are a DIY fix.
 
Last edited:
How can I gently steer the engineer in the right direction please? As I’ve said I’ve had three different engineers look at the symptoms live and none of them had any ideas thus my coming here.
 
The best advice I can give you is to put your current service provider on notice to either fix it or if they cannot, to involve the boiler manufacturer ( Potterton).

Don’t give up, all the service providers have some first class people - you just need to escalate the problem to get them engaged to fix it.
 
Last edited:
I thought I’d follow up in case someone else has similar symptoms and is struggling to get them addressed.
Firstly I will clarify the symptoms - the boiler cuts out be it for call for heat or hot water. With hot water it cuts out almost always and almost immediately whereas with heating it is less evident but does happen.
The cause was the water pump that was on its way out and did not circulate water fast enough. This only became apparent once it started pumping water intermittently rather than continuously. Changing the pump transformed the heating system completely and it became evident that it was on its way out for at least the last 3 years.
In the process of troubleshooting various heating engineers replaced the electrodes, the gas valve and the PCB.
 

Reply to False call for hot water in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
125
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
276
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
132
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock