Discuss Worcester greenstar, Hot water intermittent. in the Gas Engineers Forum area at PlumbersForums.net

Ted808

Plumbers Arms member
Plumber
Gas Engineer
Messages
359
Heating works and hot water- sometimes, but I noticed when I turn the hot tap on the pressure gauge drops to zero.
I've not seen this before. Topping up the pressure doesn't seem to make a difference. As soon as the heating only is on pressure goes back up to 1.5bar.
The thing is the flat is disgustingly filthy and I don't want to spend ages there... So if anyone has any pointers- much appreciated.

I'm thinking dirty line to PG and PV flat. Now can you get a blockage between the PG and the HW path only?
 
Check the diverter flap isn’t stuck
Check when hot water is running no flow is going down the htg flow

Other than the flow switch or plate it should work

Never need the guage go to zero on one tho then back to normal
 
Check the diverter flap isn’t stuck
Check when hot water is running no flow is going down the htg flow

Other than the flow switch or plate it should work

Never need the guage go to zero on one tho then back to normal
Yeah I've never seen that either. Can't fathom it.
 
I can't think of a single-component cause but, if I've understood the OP's observations correctly and the pressure changes are relatively rapid, a combination of faulty expansion vessel and a PRV that is passing at 1.5 bar might fit the bill.
 

Reply to Worcester greenstar, Hot water intermittent. in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

I want to reconnect some outbuildings to an existing water supply. The supply pipe is old 22mm MDPE and buried for a fair distance so not going to dig it up and replace it 😬. Question is can I use normal 22mm plumbing push-fit connectors to make the connection as finding 22mm MDPE fittings...
Replies
1
Views
262
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
241
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
318
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock