Ok guys been having to top up on a regular basis then at 1.8 bar u turn on heating and the pressure goes to 3.5 bar and flashes

Replaced the vessel and said pressure release valve also as was leaking what's more worrying is the water in system is black and contaminated and he is reporting this and another division of valiant wil be in touch re estimate for flush (magnetic)

I thought the black stuff was the inhibitor ? He's said it's oil etc and outwith the tolerance

Assume I need to get this done or warranty nil and void ? Anyone got idea on cost ? This is fairly new full system
 
Last edited by a moderator:
Who installed your boiler and how long ago? The "Black stuff" is magnetite which is a by product of the corrosion process. Your system should have been flushed and treated with inhibitor during the installation.
You will need this rectified or Vaillant will not honour the warranty. You can expect a rough cost of between £250 -£400 depending how big the system is.
 
Was installed less than a year ago I low the inhibitor definately went in as it smells like Indian spicy food. I actually bled a rad other day and water was mirky brown/ black

Hometeam called there £485 plus vat needs powerflush saying readings over 1500 should be 200 or 300 on water and requires heat exchange but will not do till sorted

Homteam telling me they use specialist equipment and takes 5 hours

Help anyone in Glasgow area
 
Last edited by a moderator:
Foxyuk , might be better off stick a post in the " i need a plumber " section

dont know on prices up your way or how big the system is but if its a standard 3 bed semi down here youd be looking at 300-350 - ish
 
Foxyuk , might be better off stick a post in the " i need a plumber " section

dont know on prices up your way or how big the system is but if its a standard 3 bed semi down here youd be looking at 300-350 - ish

It's 9 radiators 2 bedroom one level bungalow , what is involved in the process ?
 
basically the will bring a mcahin in to clean the system out , add/remove certain chemicals
 
basically the will bring a mcahin in to clean the system out , add/remove certain chemicals

Does all heating engineers carry this machine u are implying about ? My concern is that it has to be done to a certain water quality as heat exchanger will not be replaced till sorted and assume I can't get a service call

I have made contact with the chump that installed system whom is calling me back tonight at end of say is his fault but I gave no confidence in him and want it done right not a fill up the system 3/4 times put in chemicals them tell me that's it
 
i dont know how many carry the machines some will own ,othesr will hire
 
Allow plenty of time for the powerflusher's visit, it could well take a lot longer than 5 hours. My worst was 8, but i know a crew who were at it for 12 hours before they got all the much out.

I only PF for a fixed price clients think its expensive until they hear you telling the Mrs you're still at it and wont be home for tea until the job is done.
 
Status
Not open for further replies.

Reply to Valiant 837 , valiant engineer reports system contaminated. Help in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
462
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock