Christopher buzzard

Gas Engineer
Messages
190
Can some please identify the valve on this underfloor manifold ( with the black wire coming out of the top). Have an issue where the system is turning off every 10-20 minutes and staying off for a while then coming back on again. The room can’t get up to temperature because of this. Power was going to the valve but not out of it.
‘thanks for your help.
 

Attachments

  • 60D0F2CE-8DB2-4E0F-8C99-869D1D955135.jpeg
    60D0F2CE-8DB2-4E0F-8C99-869D1D955135.jpeg
    116.7 KB · Views: 19
It looks like an temperature sensor on the heating outlet of the pump.
If the temperature gets too hot the pump will stop operating - to protect the UFH pipe and the floor.

Adjust the mixing valve to get cooler water or it could be a faulty thermostat sensor
 
Hey. That’s for your reply. Must be the sensor faulty then as the thermostatic control on the flow in, was working ok And controlling the temperature. I linked it out last night just to prove there was no other issue. Going back in today to see if the room is up to temperature.
 
Christopher,

That is a TM manifold, the originally fitted high limit stat will be hard to source. The current Uponor part number is 1002371 - which may need a threaded insert to fit.

Don’t be tempted to just bypass the limit switch
 
So only there if the thermostat head on the flow, fails and or if the boiler thermostat fails?
Never seen them on a manifold before. Spoke with an electrician who said in the past he hasn’t wired them in. (Not saying he’s right to do that though)
 
So only there if the thermostat head on the flow, fails and or if the boiler thermostat fails?
Never seen them on a manifold before. Spoke with an electrician who said in the past he hasn’t wired them in. (Not saying he’s right to do that though)

Yes in the event of flow temperature being too high due to whatever reason this will isolate supply to protect floors and pipework as said above.
 
Brambles is the man on these so he is worth listening to lol. As he said linking out is not advisable, in many cases will give a quick fix or in this case find a fault but it shouldn't be left like that.
 

Reply to Uponor underfloor heating valve. in the USA area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...