got a strange one here, back boiler cravety hot water, builder wants me to fitt uf heating in the extion, so i will have to fitt two zone valves one for the new heating and one for exasting but how do i get the boiler to come on with out setting the pump away? when i just want hot water, bear in mind the boiler will have to come on when either of the valves open, has got me stuck
 
got a strange one here, back boiler cravety hot water, builder wants me to fitt uf heating in the extion, so i will have to fitt two zone valves one for the new heating and one for exasting but how do i get the boiler to come on with out setting the pump away? when i just want hot water, bear in mind the boiler will have to come on when either of the valves open, has got me stuck
is this a cryptic note to the one they call redsaw
 
Last edited:
Add a 28mm zone valve onto the gravity hot water and wire it as a C plan plus adding two zone valves for heating. As long as the orange switched wires on the heating valves are commoned you can have separate time switches etc. Think of it as though the brown wire connects to the switch live from your underfloor circuit.
 