Messages
64
If a radiator has been correctly sized for a room and the boiler is adequate and fully functioning, at what rate of C/Hour would you want a living room to be able to heat up at?

Thanks.
 
Normally, you will get/buy a pair of radiator vaves, one will have a plastic wheel head with which you can open and shut as required, the other (return end, recommende) will also have a plastic wheel head but this is only a cover and turning it has no effect, you just pull this up and open and shut this valve with a adjustable spanner, if your system is balanced then this valve will be set to 1/16,1/4,/1/2, or whatever open and don't touch this again, hence the lockshield name, you just the replace the plastic cap and if you wish to shut off the rad you just shut the the other one, when its reopened then the rad is still balanced.

You said
"At the larger value side (thermostatic) I measured a temperature of 54.2 C and at the smaller value side a temperature of 56.7 C. There were sometimes variations, but generally it's about 2.5 C colder on the thermostatic valve side "
This means to me that you have a thermostatic radiator valve (TRV) installed on the return and a wheelhead valve at the flow end, normally, it is recommended that the TRV is fitted on the flow side and the wheelhead on the return, they can be installed as yours appear to be but then the TRV must be of the bi directional type, ie, two arrows on the valve body, some installers here say that even if bi directional that they should always be installed on the flow side, mine are all on the return.
Can you post a pic of both to make sure we are talking about the same thing?
 

The link above shows the valves which I have installed.


I've had a look and I do not see any arrow(s) indicating any direction. I re-took the time for how long it takes the rad to get to maximum temperature when the heating is already fired up, and it takes up to 20 minutes for the radiator to reach maximum temperature.

I re-took the temperature at the valve ends and I get:
53 C at the TRV end, and 57.10 C at the lock-shield valve.

So:
a) I'm consistently getting a higher temperature at the lockshield end
b) the retailer states that they "always recommend installing the wheel head on the flow in and the lock-shield on the return"
c) I do not see any directional arrows
d) the rad itself can have the flow/return attached to either side

So perhaps it could be concluded that the valves are not bi-directional, and that the flow/return pipes have been attached to the wrong valves?
 
Your pipework is OK as the rad has no special instructions, the TRV and the Lockshield should be swapped, ie the TRV on the flow & lockshield on return but what actual difference this makes to the flow I've no idea, perhaps none. I've never seen that type of TRV and looking at its spec it doesn't say Bi directional but I would suspect not.

Heat up time of 20 minutes seems very long but again if these are cast iron maybe normal, I'm sure some one on here can advise, the measured flow/return temps of 57.1C/53C, with a deltaT of 4.1C even though still low IMO are possible but if its not normal for the rads to take this 20 minutes heat up time then the hot water may be partly short circuiting and not giving you the output of a 35 deg rad, ie 5177 BTU or 1.52kw.

Practically speaking my only suggestion is to get hold of a oil filled rad or equivalent, turn off the rad, set the electric heater to whatever power settings are available and that should point you in the right direction. My oil filled rad has three settings, 0.8kw(2730BTU), 1.2kw(4094BTU) and 2kw(6824BTU)
 
Heat up time of 20 minutes seems very long but again if these are cast iron maybe normal, I'm sure some one on here can advise,
It's a steel radiator, just in the style of a traditional column rad.

Practically speaking my only suggestion is to get hold of a oil filled rad or equivalent, turn off the rad, set the electric heater to whatever power settings are available and that should point you in the right direction. My oil filled rad has three settings, 0.8kw(2730BTU), 1.2kw(4094BTU) and 2kw(6824BTU)

Do you mean an electric oil-filled rad which has an electrical plug which is plugged into the electrical socket on the wall and is unconnected to the central heating system?
 
Yes, any kind of electric heater of known power that you plug in to get a comparison, I can't think of any other way.
Okay; thanks very much.
[automerge]1607356724[/automerge]
Yes, any kind of electric heater of known power that you plug in to get a comparison

I might just get a convection heater, as opposed to an oil-filled one, as they appear to be cheaper. That is, unless there's any reason why not.

This one has the three settings of 0.75, 1.25 and 2.0 kW.

 
Last edited:
That should do the job and you can't go wrong for £20.

For interest, I have one of my rads (1.6kw) shut off for the past hour or so, when fully cool I will time it to reach full temperature again.
[automerge]1607373674[/automerge]
With a room temperature of 20.3C and "cold" rad at 22C, it took 12 minutes to fully heat up. I would imagine that if the room was cold that the rad would take a few minutes more so ~ 15/17 minutes so perhaps your rad heating time isn't that outrageous.
My rad is a K2.
 
Last edited:
So, I've used a 2 kW heater without the fan on so as to make it as similar to the radiator as possible. I placed it at the same room location as the rad.

I've had the heating off in that room so the unheated room had a temperature of 11 C. It took 2.5 hours to get the room temperature up to 20 C.

The heater cut out at 20 C, so presumably the thermostat cut in. I turned the heater off at this point so that I could determine how quickly the room temperature then dropped. It dropped from 20 C to 15 C in 1 hour.
 
With a high flow through it and a high return temp, this radiator will increase return temperature at the boiler substantially. What is the return pipe temperature at the boiler? If your whole system was balanced so each radiator had a 15deg drop you might surprisingly be able to increase boiler flow temp yet lower return temp so increasing overall efficiency.

I am a bit surprised that with one external wall that is insulated this room temp drops to 11 deg overnight. Is the whole house cold? Are the properties next door empty? Sort that window!
 
So, I've used a 2 kW heater without the fan on so as to make it as similar to the radiator as possible. I placed it at the same room location as the rad.

I've had the heating off in that room so the unheated room had a temperature of 11 C. It took 2.5 hours to get the room temperature up to 20 C.

The heater cut out at 20 C, so presumably the thermostat cut in. I turned the heater off at this point so that I could determine how quickly the room temperature then dropped. It dropped from 20 C to 15 C in 1 hour.

Increase your boiler set point to 75C, this should give you a 2.4 kw rad based on the 50 deg rating, if its "only" producing" 2.0 kw it should still heat up your room in 2.5 hrs. Once you have a rough idea of what these column rads are actually producing then combined with the window mod as suggested, may mean that you can retain this rad with a boiler temp of 60/65C.
 
With a high flow through it and a high return temp, this radiator will increase return temperature at the boiler substantially. What is the return pipe temperature at the boiler?
I know there are several pipes connected to the underside of the gas boiler. I could easily take the temperature with the contactless thermometer, however I wouldn't know which is the return pipe, or how this could be determined.

If your whole system was balanced so each radiator had a 15deg drop you might surprisingly be able to increase boiler flow temp yet lower return temp so increasing overall efficiency.
I'll look into that then.

I am a bit surprised that with one external wall that is insulated this room temp drops to 11 deg overnight. Is the whole house cold? Are the properties next door empty? Sort that window!
There are people in the properties next door. I think one particular issue with this room, is that I have removed all the paint from the timber window frame in order to re-paint. It was previously painted closed over decades and this may have helped keep cold air out!

Increase your boiler set point to 75C, this should give you a 2.4 kw rad based on the 50 deg rating, if its "only" producing" 2.0 kw it should still heat up your room in 2.5 hrs. Once you have a rough idea of what these column rads are actually producing then combined with the window mod as suggested, may mean that you can retain this rad with a boiler temp of 60/65C.
I have done this and set the boiler temperature to 75 C for the heating system. Starting with a room temperature of 12 C, it took 4.5 hours to get up to 21 C.

When I did this for the 2.4 kW heater yesterday the room temp started at 11 C and took 2.5 hours.
 
Well, if a 2 kw electric heater got the temp up in 2.5 hours and a "2.4" kw column rad takes 4.5 hours then its pretty obvious that its not producing 2.4 kw for whatever reason, maybe original spec very optimistic as someone stated so what options now?
 
I know there are several pipes connected to the underside of the gas boiler
The hottest pipe is the flow probably 22mm copper. Next hottest is the return. Often at opposite ends of the boiler. Measure after boiler on for 30 min or so.

The problem is your window, that's all.
[automerge]1607464690[/automerge]
Well, if a 2 kw electric heater got the temp up in 2.5 hours and a "2.4" kw column rad takes 4.5 hours then its pretty obvious that its not producing 2.4 kw for whatever reason, maybe original spec very optimistic as someone stated so what options now?
Perhaps return temp too high so boiler modulating down?
 
Last edited:
Well, if a 2 kw electric heater got the temp up in 2.5 hours and a "2.4" kw column rad takes 4.5 hours then its pretty obvious that its not producing 2.4 kw for whatever reason, maybe original spec very optimistic as someone stated so what options now?
I could look into the temperature drop issue referred to by gpbeck above. Though even if this is sorted, perhaps it won't make the major improvement which would be required.

It's possible to get a similar style of rad and similar size, but a different brand. This may be an option.


[automerge]1607464889[/automerge]
The hottest pipe is the flow probably 22mm copper. Next hottest is the return. Often at opposite ends of the boiler. Measure after boiler on for 30 min or so.

I shall look at that.
 