We have this boiler installed and it's started to give issues.
The service was done and passed ok. But only as there was no noise for the guy to hear.
Radiators are fine.
When hot water is being used it generally seems OK, but sometimes there's a large rumble noise 10-15 secs then it stops.
I haven't been close at this time but have also noticed when showering the boiler setpoint is exceeded. Flame cuts out. Drops temp,and refires. Temp increases, exceeds and flame cuts out.
The expansion vessel is at 1bar so doesn't seem it's that, but other than calling baxi. What can I check next?
Video to show the temp fluctuations available.


Thankw
 

John.g

Messages
3,822
Could be the PHEX (plate heat exchanger) is fouled, it may run OK at low HW demand but trip out on high demand.
"have also noticed when showering the boiler setpoint is exceeded" Is this the DHW setpoint thats exceeded by the actual DHW temperature?. If so could be different problem. Can you run two HW taps at full (HW) flow and see if the same problem occurs.
 
D

Deleted member 120897

No video attached, also how old is the boiler? Could be plate hex as above, but can be other things too.
 

Knappers

Plumber
Gas Engineer
Messages
997
HEX or sensor - shouldn't be a difficult find/fix for a gas man
 

Reply to Potterton promax 40erp HW issue in the Central Heating Forum area at PlumbersForums.net

Similar threads

R
  • Question
Hi, thanks for your answer. It does not have the preheat. Kind regards, Renato
Replies
2
Views
1K
Renato
R
W
I've had someone round and I have the answer. It was the pump overrun stat, it's broken down internally (you can hear it rattle) and was providing...
Replies
27
Views
2K
West Country
W
P
Chris, just to update, thanks for all your help, dismantlEd the Venturi was all ok, looked good and cleaned. Decided, to pay attention to the CH...
Replies
3
Views
281
Plipplop
P
S
Replies
2
Views
184
ShaunCorbs
ShaunCorbs
H
Reporting back finally ... For the benefit of anyone coming to this on a later search over a similar issue/solution, the problem is fixed though...
Replies
8
Views
509
Hannay
H
Creating content since 2001. Untold Media.

Newest Threads (Please Reply)

Search Forum

Top