Sorry. Thought we were in a compartment. :(

44kw?
(44-7)*5=185cm2.
The complication of fly screens reducing free air is irrelevant, in as far as they cannot be present
 
Sorry. Thought we were in a compartment. :(

44kw?
(44-7)*5=185cm2.
The complication of fly screens reducing free air is irrelevant, in as far as they cannot be present
It's not irrelevant I said he needs to check that vent as that type has a fly screen if so he needs to remove and replace the vent.
 
It's not irrelevant I said he needs to check that vent as that type has a fly screen if so he needs to remove and replace the vent.

I apologise. I misconstrued your comment. I had it in my head that you meant that the calculation should be done taking the screen into account.
Obviously, fly screen awareness IS relevant, as you say.
 
well i have come across quite a few of this type over the years that have a fly screen so best to check

Plaster Vent With Fly Screen 225mm x 75mm
Agreed. There were many types of old plaster vents that came with a flyscreen stuck to the back as many of the louvres used to break easily when trying to remove them.

Generally when you had a plaster vent, you also had a terracotta vent on the outside which was very restrictive and passed very little air. The vents were large and generally too small; even the small holes in the terracotta were tapered so they looked smaller form the outside but were even smaller on the inside!

Again, many of these vents used to be blocked with cavity wall insulation. The flyscreen would stop it coming through the louvre and the terracotta would be so small they would just block.

All a bit negative but very relative; when you actually got a tape measure to the opening you would find many of them actually didn't have enough ventilation so best to check.
 
Generally if one of these old plastered vents us present there us usually a terracotta vent outside that passes very little air due to it's construction so I would also be looking at this also as it us in the equation and more than likely insufficient.
 

Reply to kingfisher CF 150 with aspestos flue in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello All, I was hoping you could help with a potential boiler build query for my father. He has recently had a new boiler installed via British...
Replies
5
Views
241
https://www.telegraph.co.uk/news/2023/05/12/the-heat-pump-farce-has-finally-been-exposed/?li_source=LI&li_medium=liftigniter-rhr I realise not...
Replies
16
Views
2K
Does a window need to be atleast 30cm away from the base of the boiler flu (the part that comes out of the wall/opening) or the end of the flue...
Replies
3
Views
2K
    • Like
Hi all, We recently purchased a house and nothing seems to work correctly here, I've spent weeks rectifying issues. Plumbing, electrical...
Replies
47
Views
5K
Hello all, I should start off by stating that I'm not in the industry - I'm just a DIYer with a "what-if" idea. Hybrid systems and solar...
Replies
6
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock