Does anyone work or install gas Agas, just wanted a rough gas consumption for an older 2 oven 3 ring pf type can't get on site till later, it's my brother in laws place. Ha had a green star 40cdi fitted, got an existing Aga and a Drugasar built in gas fire, called yesterday, looking for something else in the garage and then noticed a U6 with 22mm running to the boiler which is the first appliance some 10 metres away. Didn't want to jump in and say not big enough without facts.
cheers.
 
they are quite low gas rates on agas about 5KW link too site Mi's [DLMURL]http://www.rayburn-web.co.uk/Prodin/Aga%20current%20cookers/Aga%20Gas%202%20and%204%20oven%20PF/Aga%20Gas%202%20and%204%20ov%20PF%20inst%2009-10.%20EINS%20511112.pdf[/DLMURL]
 
Last edited by a moderator:
Cheers Gasmk1 I googled gas Aga and didn't think of Rayburn, 5 kW still puts the pipework too small, the fire is about 7kw plus the 40 cdi should be bigger than 22mm.
I don't do relatives saves all kind of hassle, but will go out if they have problems, just won't do installs etc.
 