Boiler NO 81? should now be be running at 65C/0.39M3/hr (flow) and rad(s) output of 59% OR
55C/0.77M3/hr (flow) and rad(s) output of 48%.
and Shaun's condensate flow at roughly 0.7 lit/hr @ 20 kw boiler output or pro rata.
 
Last edited:
I thought the same thing as John mentioned, when the boiler first fires up in the morning, return temperature is typically 20-25oC & after it cuts out on the room stat, may not restart for 1-2 hours, then again very low return temperature for some time ( will try and monitor return temperature next time it restarts, be interesting to see the climb rate and how long it ‘ should be’ condensing for. So going back to deposits on the heat exchanger wouldn't these periods of heavy condensing keep the exchanger clean ? I am running my boiler outlet at 64oC, i tried 62oC, but even 2oC seemed to make noticeable difference to radiator heat output. The return temperature when steady and modulating is 53-56oC. As I said previously I was considering replacing 2 lounge radiators with double fin, but looks like the best I might get is a 45oC return temperature.....only an educated guess.....which would give a 3% saving, would take around 20-25 years to pay back the cost..so very likely going to abandon that idea.

I know I may get shouted at, but I dont suppose I could clean the heat exchanger myself, I think it will need a Gas Safe person most likely.......

there is a move to make manufacturers add an efficiency display to their boilers and show when it’s in condensing mode, I think they will fight hard against this, as people will soon realise they are not getting the 97% efficiency that they expect..

take care all & keep safe 😎
 
I maybe thinking wrong but how can 2dc make a room feel colder when it’s well above the room temperature

I could understand if the flow temp was 40 but not 60dc you sure you have a flow temp at 62dc at all your trvs ?
 
I maybe thinking wrong but how can 2dc make a room feel colder when it’s well above the room temperature

I could understand if the flow temp was 40 but not 60dc you sure you have a flow temp at 62dc at all your trvs ?
Hello, there must come a flow temperature that just doesn’t release enough heat to be comfortable, not sure if flow temperature and radiator heat release is linear. Just seeemed to make a difference when I lowered it to 62oC.....no idea if its the same temperature at the TRVs all rads do get hot, so assume that must be the case.....

also at 62oC the boiler often cuts out at 65oC as it can’t reduce below 5KW......

very happy with how it’s running now, have had some excellent advice and learnt lots in the process.....

thanks
 
This thread has thrown up some extraordinary "facts" re flowtemps/flowrates and their effect on return temps etc.

Any temperature change in either flow or room temp will have a effect on rad output but its not linear, it works with a exponent of 1.3 where the rad output is based on the ((meanradtemp)-requiredroomtemp))^1.3.

Using your observations above, initially I calculated that the 4/5 rads that you have running at a fixed flow of 0.76M3/hr......
flow/return/rad output 65C/59C/5.21kw. Now reduce the flowtemp to 63C results in........
63C/57.4C/4.9kw (which is why your boiler is cycling), you are running right at the switch point because you require the rads to run at ~ 68% of their rated output so running very close to the minimum boiler output.
If you require a rad output of 5.21kw with that 63C flowtemp then the flowrate would have to be increased from 0.76M3/hr to 2.24M3/hr, (impossible) and you would achieve 63C/61C/5.21kw.

If you had TRVs on these rads and increased the flowtemp to 75C then they would have throttled in to give 75C/48.8C/5.21kw at a very reduced flowrate of 0.17M3/hr. rad&boiler deltaT of 26.2C, OK if boiler is running but flow too low for the 1 minute fire up requirement of 9.6kw.

The above might look a bit complicated but very easy to calculate in a spreadsheet I made.
 
Last edited:
Should also add another bit of info.
If your room(s) should suddenly fall to 10C then the flow/return/output will be
65C/56.6C/7.35kw. 5C roomtemp = 65C/55.6C/8.21kw & 0C = 65C/54.4C/10.6kw.
The most interesting part of all this is that the return temp doesn't change much in any of the above so it looks like any system with fixed flow temp and fixed flowrate will never condense under any conditions except at start up
 
Very interesting John, would love to see the spreadsheet, always making these for all sorts of things......thanks
Should also add another bit of info.
If your room(s) should suddenly fall to 10C then the flow/return/output will be
65C/56.6C/7.35kw. 5C roomtemp = 65C/55.6C/8.21kw & 0C = 65C/54.4C/10.6kw.
The most interesting part of all this is that the return temp doesn't change much in any of the above so it looks like any system with fixed flow temp and fixed flowrate will never condense under any conditions except at start up
interesting stuff 👍 would love to se your spreadsheet, can you attach ?
 
I will try once again but for the past few months havn't been able to attach any, they used to attach no problem previously in zipped form.
 