does the burner modulate? whats the flow temp like compaired to the return? is the return filter blocked?
how do i access it,can i isolate then remove or is it a drain down,nothing in mi.....will do regarding fga...taits fitted to the return iso valve also check fga settings
i'll have a look tommorrow ta...on a different boiler fitting a worcester junior i 28kw,it came with a low nox chip, whats the benefits with lowering nox levels if any...?turn off RH return side iso if it has a built in loop crack the nut bolted to the iso and bleed into a bowl then remove the nut filters behind it if theres no built in loop it will be a silver cap
less harmful pocs into the environmenti'll have a look tommorrow ta...on a different boiler fitting a worcester junior i 28kw,it came with a low nox chip, whats the benefits with lowering nox levels if any...?
why the choice ,why not fitted as standard,..strange.less harmful pocs into the environment
i went back to this boiler and gas was fine co% 8.7 all good,the boiler when first knocked on runs fine until temp is reached ,then it just cycles constantly,down stairs is in 15mm on flow and return, upstairs is in 8mm and on all rads the flow is red hot and the return is cool,could this be due to a blockage on the main return pipework,and could the ch ntc be faulty causing these symptomsnot sure dont fit worcesters just fix them when they die,leak,blow up etc
yes filter okdid you clean the filter? thermister does not point to this
yes rf stat baxi's ownhas it got a external room stat?