Mornin.... Had a phone call off me mate this mornin with his boiler failing as above....i know 9 times outta 10 with an e168 fault would be a pcb fault but as its only happenin on hw and not ch would you still chuck in a pcb? Cant be arsed to go round on a sunday to check.
Its constantly goin to...
note you dont need to do this every year but the customer wanted a new seal (friends of theres has a vailant melt) now firstly its assumed your not a halfwit and have isolated the gas and electric first so if you electrocute yourself or blow the house up its your problem
1,remove combustion door...
You may have seen on other threads that Baxi are now offering a 7 year warranty* on their Duotec HE A combis - thats the new name for the original Duotec, not to be confused with the Duotec GA which is a different beast.
We have bought a heap of them, and have the following offer until the end...
Has anyone bought one of the Baxi Duotec HE A combis recently - the one with the 7 year warranty, not the GA heap?
It would be a great help to me to know how much you paid for it, where from, which model, and whether it came with any extras.
Either on this thread, or by PM.
I'm negotiating...
Hello just received call from customer above boiler e133 error which I see is ignition error, looking at the fault finding in the mi it requires 100 v dc at terminals 2 and 7 if not then new pcb. Please could anyone offer any more assistance in diagnosing. Thanx in advance
serviced one this wk - was a nice install only problem the condense come down 4" then through wall in 32mm very tidy but impossiple to remove the condense sump without cutting the pipe and refitting with coupler ok this time but not possible next year due to no space for another coupler - bad design
I'm posting this in the arms, because I am not sure that Baxi have gone public yet.
A little birdy tells me that the old Duotec 1 will be promoted from Feb - Dec 2013 with a 7 year warranty...
... but at the moment they don't have any stock!
what a day i go to a duotec prv blowing off - find vessel has no air to re charge it to 1 bar and boiler ok on way to next job van breaks down - get van sorted by 5pm then get a call the duo tec is making noises in hw mode and the water is hot and cold. get there and the boiler fires on hw and...
I posted earlier about our hot water cycling on and off but now its got worse :(
When a hot water tap is opened, water starts to flow, the boiler fires up and the boiler temp display goes up slowly to around 60 degrees, all as usual, and the water gets warm. Then, the boiler temp starts to...
bobnlibby
Thread
baxi
boiler
cold
degrees
duotec
exchanger
hot
hot water
starts
water
anybody come across a problem ive had with the duo-tec 2 all fitted and working perfect so come to do analyser test going thro that ,all good ,then suddenly my analyser goes off the scale, high co 1100 ppm ect press escape and it just goes back to to normal it comes back down to normal quickly...
been to this today got error e 160 pump runs but fan does not. 240v to fan and neutral and earth to fan ok. removed the sensing 4 way plug and got continuity on each of the 4 wires from the board to the fan.i am assuming its the fan . spoke to baxi but got someone just reading off script. what...
Hi,
Have a bit of a strange problem with a baxi duotec 28. When the CH is turned on the pressure instantly drops by 1/2 bar. All rads get hot and seems to be working fine. Over several weeks the pressure is gradually dropping so needs topping up. The expansion vessel is fine and there are no...
owington
Thread
baxi
drop
dropping
duotec
instant
pressure
pressure drop
turned
weeks
Thinking of installing a Baxi DuoTec (Mk2) 40 GA... Have read various negative reviews on here of the new Baxis, but was wondering if anyone actually has anything positive to say about them?!
Flow-rate seems very good for the 40kW version (16 l/min?).
More importantly, is their 5-year...
So, fitted approx 4 new neta tec's this year. As I liked the duo tec I thought I'd carry on the tradition and try them, I've read posts and imputed my take on them... overall, I like them. But now I've just had a call from second gas valve failure,( which was fitted approx 3 months ago) With...
just had a call about 5 mins ago tenents saying boiler is e168 flashing up i think this is a pcb fault is there any checks to do, im going first thing in the morning thanks
just had a call about 5 mins ago tenents saying boiler is e168 flashing up i think this is a pcb fault is there any checks to do, im going first thing in the morning thanks
customer is looking at getting a new gas system boiler, im not fitting incase any asking. but he and i dont know what these boilers are like
suppilers are saying that in the past baxi got a bad name for past boilers but there new ones are good.
has anyone any experience of the new baxi boilers...
mark_mc
Thread
baxi
boiler
duotec
megaflow
oil
system
system boiler
Installed recently, display is flashing error code 83(not in manual) and showing spanner symbol which means cannot be reset by user, contact installer or heateam. Does anyone know what fault code might be? is there anyway i can reset the boiler without calling heatteam as i'd like to get elderly...
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.