Discuss how to service a baxi duotec 1 or HEA in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
B

Billy Bob Bob

note you dont need to do this every year but the customer wanted a new seal (friends of theres has a vailant melt) now firstly its assumed your not a halfwit and have isolated the gas and electric first so if you electrocute yourself or blow the house up its your problem
1,remove combustion door
2,disconect the gas to manifold nut
3,remove the spark,detection and earth leads
4,remove the clear silicone equilibrium pressure tube note its position get it wrong and the boiler wont fire afterwards
5,remove the fan electrical connections
6,remove the 4 10mm front cover/hex nuts
7,carefully pull the whole assembly forwards the venturi will drop out of the gas to manifold connection keep this safe and dont forget to refit it
 

Attachments

  • WP_20131004_001[1].jpg
    WP_20131004_001[1].jpg
    87.5 KB · Views: 38
  • WP_20131004_002[1].jpg
    WP_20131004_002[1].jpg
    86.5 KB · Views: 40
  • WP_20131004_003[1].jpg
    WP_20131004_003[1].jpg
    86.2 KB · Views: 38
  • WP_20131004_004[1].jpg
    WP_20131004_004[1].jpg
    89.3 KB · Views: 35
  • WP_20131004_005[1].jpg
    WP_20131004_005[1].jpg
    88.7 KB · Views: 34
  • WP_20131004_006[1].jpg
    WP_20131004_006[1].jpg
    90.9 KB · Views: 37
  • WP_20131004_007[1].jpg
    WP_20131004_007[1].jpg
    91.3 KB · Views: 36
Last edited by a moderator:
Re: how to service a duotec HEA

pour some water through the hex to make sure the condys clear,note the condition of the electrodes if they are bending they need replacing
 

Attachments

  • WP_20131004_008[1].jpg
    WP_20131004_008[1].jpg
    100 KB · Views: 31
  • WP_20131004_009[1].jpg
    WP_20131004_009[1].jpg
    98.1 KB · Views: 30
  • WP_20131004_011[1].jpg
    WP_20131004_011[1].jpg
    95.2 KB · Views: 31
  • WP_20131004_012[1].jpg
    WP_20131004_012[1].jpg
    87.9 KB · Views: 27
  • WP_20131004_015[1].jpg
    WP_20131004_015[1].jpg
    94.8 KB · Views: 30
  • WP_20131004_019[1].jpg
    WP_20131004_019[1].jpg
    88.8 KB · Views: 31
  • WP_20131004_020[1].jpg
    WP_20131004_020[1].jpg
    90.7 KB · Views: 31
Re: how to service a duotec HEA

closed thread may make it sticky
 
Re: how to service a duotec HEA

finally change the gasket,reassemble ,LDF both the gas to manifold nut and just in case the gas valve nut,put it into calibration mode and carry out a fga,PN of the gasket in the photo
 