Have you tried a flowcup ash to see if its as per manufacturer flowrate .
Discuss Ideal logic 30 combi. HW issue in the Plumbing Jobs | The Job-board area at PlumbersForums.net
So you have a solid red light on the hall sensor all of the time during hot water. Amd you have good flow from the tap ?
Have you taken the turbine out and cleaned it.
Also have you cleaned the flow regulator and filter ?
Both thermistors should be
At 60 degrees"ish 2500ohm
at 85 degreesish 1000ohm
If they are wildly different then replace.
And at 75% tap opening its gas rating fine. And with the hot tap wide open its still gas rating fine - no drop off ?
Only other thing is tap max flow is more than the boiler can heat
what descaler did you use? only real strong acid gets rid of all the crap i.e sulphuric
sounds like the plate is just blocked
Have you tried a flowcup ash to see if its as per manufacturer flowrate .
Have you tried a flowcup ash to see if its as per manufacturer flowrate .
This is the only way of determining whether the boiler is working as per the spec. The cold incoming water temp in the winter makes the hot water cooler. Check the manual for what temperature rise you should be getting at what flow rate, so like 11 l/min at 35 degree temp rise. The incoming main will be about 10 degrees roughly at this time of year so with a flow of 11l/min you should see a water temp of 45 degrees as an example.
Exactly, if the flow is higher then the temperature rise will be less resulting in lower temperature water. Manufacturers normally quote either a 35 or 40 degree temp rise.
Get your flow cup and digital thermometer out to confirm.
Exactly, if the flow is higher then the temperature rise will be less resulting in lower temperature water. Manufacturers normally quote either a 35 or 40 degree temp rise.
Get your flow cup and digital thermometer out to confirm.
As above, easiest way is to restrict the flow going into the boiler or alternatively just advise the customer on the limitations of their boiler. Understanding how it works will enable them to get water at the temperature they desire.
As above, easiest way is to restrict the flow going into the boiler or alternatively just advise the customer on the limitations of their boiler. Understanding how it works will enable them to get water at the temperature they desire.