nysk2008

having a hard time on this job, replaced pcb as not working and all good. cust calls and o/h is now tripping about every few hours, replaced old board with new updated board - anyone had this issue or know of it?

cheers
 
Is it fully pumped or gravity hot water mysk? Could be wiring wrong if link left in. However if it's overheating then you need to know flow temp. Could well be a faulty control stat or o/heat stat?
 
Hi Diamond, pumped ch, gravity hw, no link on wiring but contol stat did seem dodgy. didnt get any m/meter readings as i had left
Is it fully pumped or gravity hot water mysk? Could be wiring wrong if link left in. However if it's overheating then you need to know flow temp. Could well be a faulty control stat or o/heat stat?
 
Check the pump over run is operating? Think it's the purple wire out the pcb.
if not could be boiler stat or heating valve sticking,
 
Hi Diamond, pumped ch, gravity hw, no link on wiring but contol stat did seem dodgy. didnt get any m/meter readings as i had left

The link k1-k2 should be present for gravity h/w pumped heating as it bi-passes the o/heat? However if it otherwise worked ok before I'd suspect control stat faulty. It's worth knowing what the flow temp is getting up to however, a tell tale complain't from the custard is water and rads getting very hot..! :)
 
Last edited by a moderator:
Thanks diamondgas. I know for a fact here is no link currently between k1-k2 and the hw was mega hot, ill try the link then control stat, thanks again

The link k1-k2 should be present for gravity h/w pumped heating as it bi-passes the o/heat? However if it otherwise worked ok before I'd suspect control stat faulty. It's worth knowing what the flow temp is getting up to however, a tell tale complain't from the custard is water and rads getting very hot..! :)
 
Status
Not open for further replies.

Reply to overheat glowworm ultimate 40ff in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock