Hi chaps, I got a danfoss standaRd room stat. Am not getting any audibel click when turning it up or down, when heating is on, am getting 230v at terminal 4 and . Even when I turn it up and down. Is this correct? As it is not calling for heat at wiring centre. So not getting any heating. Wires are a pickle as well.
 
20130904_141244.jpg

Wiring centre
 
But apparently it was working ok. And then the heating would stay on with hot water but couldn't put heating on on its own. So I put new 3 port valve in and now I can get hot water on its own but not heating at all
 
its a take out and start again to me , bloody sparkys

It wasn't a spark it was I! Screwfix had red insulation tape on offer. I would defo strip it all back and re do all connections and clip it all back a little neater.

If its just heating u prob made minor error. Is stat a 3 wire or just live in s/l out?

So when hearing is on does vale engage / but no ignition on boiler? If so no juice getting through micro switch when 3 port swings to hearing only.

Also what boiler is it?
 
Last edited by a moderator:
Is the red live when calling for heat ? Is the black live too ? What have you checked ?
 
Yep, am getting 240volts on on both sets of wires. But if I turn stat up or down nothing changes.

Also heating on on programmer is live. But not getting any audible click from stat
 
Was warm yes and the clients said it is usually a few degrees out as they have tested it
 
I cannot find it? Think in that junction box with all the red tape. But what I thought was it was not live
 
For sake of a few quid I'd tempted to swap stat to emliminate it
 
Sorry. If u suspect stat has reached set point and thus broken the circuit, connect the two red wires together using the black jumper wire.

I'm a junkie, excuse my last post. Thought stat had two red and one black wire. Just and off the wall thought here, the programmer hasn't been set wrongly? Perhaps for a gravity system??

Also the red wire with just tape on end at boiler end could it be demand signal from 3 port? See if its live when htg only engaged on 3port? If so open stat by turning down, is it still live?

You didn't say if 3 port went over to heating and ran pump and there was no call for heat or if nothing at all happened?
 
Last edited by a moderator:
I'm a junkie, excuse my last post. Thought stat had two red and one black wire. Just and off the wall thought here, the programmer hasn't been set wrongly? Perhaps for a gravity system??

Also the red wire with just tape on end at boiler end could it be demand signal from 3 port? See if its live when htg only engaged on 3port? If so open stat by turning down, is it still live?


You didn't say if 3 port went over to heating and ran pump and there was no call for heat or if nothing at all happened?


The 3 port valve did not move at all. No live on the white wire. Also the red with tape on it was live when hot water was. Not heating
 
Remove red wire from stat. Is black still live ?

Am not there now but shall when next there.

Any chance someone can explain to me how to read a wiring diagram for a stat as I have been looking on the danfoss site and don't really understand the diagrams
 