Can anyone give me a specific way to calculate the water volume within a heating system? I'm trying to work out if an existing installation would benefit from an expansion vessel.
 
Heating load wise on domestic its 6 litres per KW heat load so 18kw heat only would be 12kw x 6l = 72L in commecial its 10-12 litres per kw of heat depending on the type of output, ie underfloor or steel panel rads.
 
Heating load wise on domestic its 6 litres per KW heat load so 18kw heat only would be 12kw x 6l = 72L in commecial its 10-12 litres per kw of heat depending on the type of output, ie underfloor or steel panel rads.
72L expansion vesel for a 18kw on the heating ???
 
I'm not sure that that there will be an accurate formula because the length and diameter of pipe runs would be an unknown.
If in fact you did know the true volume of a system then you could work out the size of vessel required but you would always add on a bit for luck.
 
Bang in a 12 litre for a normal house,if the prv starts discharging,look em in the eye and tell a lie...... ''Must be due to Hard water guvoner''

And by the way, the system now needs a powerflush lol
 
if it starts discharging just stick a 6 bar one ( from another post leaking prv):)lol
When i first saw the discharge pipe on a logic i thought it had been capped off by a DIYer,i was going to knock on the door and warn them of impending doom.... when i fitted my first a week later i was so glad i didnt
 
so what your basically saying is, a 3 bed house just stick in a 12 litre expansion vessel?
 
If the existing vessel is sound and the pressure is rising excessively when heating up whack another one in? an Additional 8 litres should suit most applications?

Or do you want water content per metre info?
 
if its a small 3 bedder i bang in a 8,if its larger i normally go for a 12.
think of it as not an exact science as many combi's only have 8 litre fitted,this will do most homes,but sometimes on a big house you have to fit additional expansion vessel,have seen the maths to work out vessel size,but on housing you dont have to be spot on,as combi,s are an example,but as said before on a big commercial job you would have to work it out
 
If the existing vessel is sound and the pressure is rising excessively when heating up whack another one in? an Additional 8 litres should suit most applications?

Or do you want water content per metre info?
spot on ,normally if space is tight a pull out the old vessel and bang in a 12 on sealed symstems,did water content years at college ago ,never remembered it.
 
Attach a hose and drain it into a bucket and see show many time you have to empty the bucket. Add a bit on if the drain is higher than the lowest point and have fun if it's a drop system!
 
Attach a hose and drain it into a bucket and see show many time you have to empty the bucket. Add a bit on if the drain is higher than the lowest point and have fun if it's a drop system!

cleaver idea I will just add 5 or 10% to this volume as you will have water left in the pipe work and bottom of rads
 
Raise the pre-charge pressure if it is near the limit for the vessel size.
 