I live in a maisonette and there is a single pipe that comes in from the street for both flats.

The pipe that enters the building is lead, probably 3/4, and is changed to 15mm copper pipe with an stopcock. This goes on for about 5-10m where it splits to both flats.

Generally, water pressue is ok, but when more than one tap is on, pressure drops significantly.

My question is, if the 15mm pipe was changed to 22, would that help to increase pressure, or would I not really notice a difference? or would it be better if the pipes were split at the point of entry instead of about 5-10m in as currently?

Thanks
 
Try the following ready reckoner:

Flow Rate Calculator - Pressure and Diameter | Copely - https://www.copely.com/tools/flow-rate-calculator/

From that I reckon the single 22mm wins over a pair of 15mm by about 50% for the lengths you suggest.

I've assumed 1 bar mains pressure ( min acceptable domestic pressure ? )

There are other calculators and the formula avail, so best do a cross check. Google "flow formula for pipe".

Cheers,

Roy (A very amateur plumber)
[automerge]1591369116[/automerge]
Try the following ready reckoner:

Flow Rate Calculator - Pressure and Diameter | Copely - https://www.copely.com/tools/flow-rate-calculator/

From that I reckon the single 22mm wins over a pair of 15mm by about 50% for the lengths you suggest.

I've assumed 1 bar mains pressure ( min acceptable domestic pressure ? )

There are other calculators and the formula avail, so best do a cross check. Google "flow formula for pipe".

Cheers,

Roy (A very amateur plumber)
P.S. I should also have said, best to use the above on a big screen comouter/tablet. Mobile works but allmresults numbers will be vertical so bit tricky to read.
 
The pipe that enters the building is lead, probably 3/4, and is changed to 15mm copper pipe with an stopcock. This goes on for about 5-10m where it splits to both flats.
Hmm. Lead pipe has quite thick walls. IIRC, 1/2" ID lead (5lb/yd) has an OD of slightly over 3/4". If I'm right, increasing the size of you current 15mm copper tube is not likely to make a significant difference because the flow will still be limited by the lead supply pipe.

You might want to get a couple of quotes for replacing the supply pipe and increasing its diameter at the same time.
 

Reply to change to 22mm pipe from mains? in the USA area at PlumbersForums.net

Similar plumbing topics

Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
232
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
324
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock