Hiya guys

I currently specing a job for a 5 bedroom house with x5 ensuites. Could anyone advise me on sizing cals for unvented cylinders.

Thank you
 
showers baths ? spec

water mains flow and pressure static and dynamic
 
ta last q how many outlets are they planning on using at once /demand like 4 showers each morning etc
 
400l or 300l fast reheat

4 showers lets say 12lpm

60/40 split

8 hot / 4 cold

average shower 10 mins

so total per shower 80l hot / 40l cold

over 4 showers 320l hot / 160l cold

if you allow this for cylinder temp will give you a bit of wiggle room as people dont have 60dc showers :D
 
i would allow a good 25kw for a high recovery

10kw for re heat within 90 mins is you can add more if the coil will take it eg 20 kw for 45 mins etc
 
Okay so I've got a Heat loss of about 24 kw for the rads including a 15% margin for pipework etc etc

The system will be run from a oil boiler, initally I have thought a 32kw would be suitable. The coil on the propsed 300 litre cylinder is 39kw.

Whats your opinion on fitting a larger boiler?
 
depends stagger the hot water times then you can go with a 28kw

if they want them both on the same time around the 40 kw mark
 
How about putting in a flow switch & timer device so that after so many mins of HW flow, the boiler automatically initiates HW reheat? That could operate in parallel with the std HW schedule.
 
How about putting in a flow switch & timer device so that after so many mins of HW flow, the boiler automatically initiates HW reheat? That could operate in parallel with the std HW schedule.

you could do how water priority ish
 
normally try and get it close to a load bearing wall or add extra support in
 
with regard locating this beast of a cylinder, 300kg odd is alot of weight do you guys do load cals for placing units like this on joists

As Shaun says, get close to a wall first. Personally, I've always put mine on 25mm ply spanning joists and screwed through into them to distribute weight as much as possible. 300KG isn't that bad. Tis only three rugby players in a huddle ;)
 
w plan system

Hot water priority, if there is a demand for hot water & heating, the hot water is heated first
Ahh. Sorry, bit of a thick day!
My point was to try to add a bit more monitoring of HW use rather than rely on fixed stat hysterisis alone. Ideally, one would replace the stat with a sensor so the two can be used in parallel. It would however require a microprocessor & programming to deliver...
 

Reply to Unvented cylinder size in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock