Air entering central heating system and hot water pumping over into make up tank in artic when h/c control is switched on. There is no problem when only c/h is on! this situation as only occurred since replacing my Grundfos UPS2 with a UPS3
I have tried the pump on different speeds . On the box that the pump came in it stated " Model A" Is there more than 1 UPS 3 models?

Any advice would be greatly appreciated.

Regards.
James
 
Can you give the exact details from the label on the UPS3, also any idea of what mode/settings you have tried, also a few photos.
Also any idea of what mode/setting the UPS2 was on, did this pump also have LEDs and a setting button.?
 
Last edited:
If the below is your pump, suggest (if not already tried) CP1, bottom right or PP2, second down on right, hold the setting button for 3 secs until LEDs start flashing, then single presses to get CP1 (3M) constant pressure, or PP2 (3.8M) proportional pressure as indicated by the flashing LEDs sequence.

1648809055353.png



1648808793685.png
 

Reply to Problems with air entering central heating system in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock