Hi All

dealing with a very nice landlord who is trying to plan the layout of a recently acquired first floor flat. The current install is a vented old school boiler that's just been condemned.

Question is what's the lowest flow and pressure you would happily install a Combi on. Testing I get 8lpm and just under 1bar I've said I'm not happy but LL is insistent that the old layout doesn't fit with her plan.

I think I know the answer but just looking for a bit of reassurance

Any thoughts.
 
It's a full bore lever from a previous partial refurb
 
Being first floor flat does it have its own main supply or is it shared from the flat/shop below?.....regards Turnpin:8:
 
Min I would is 1 bar and 12lpm

What's Pipework to lever valve ?
 
Last edited:
I'm with Shaun
12 Ltr per min minimum and 1:0 bar
Absolute minimum or you're asking for trouble
 
I'm with Shaun
12 Ltr per min minimum and 1:0 bar
Absolute minimum or you're asking for trouble
 
Thanks chaps you've confirmed what I thought. Not enough water full stop.
 
Potentially yeah I will discuss with the landlord
 
Status
Not open for further replies.

Reply to Minimum for a Combi in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m...
Replies
6
Views
326
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock