Been out to fit new heat exchanger to a keston c55. On inspection the exchanger wall was getting pretty worn and causing the outer casing to scorch. Changed heat exchanger fine. Changed ignition electrode and gaskets. On firing the fan runs, and then a pop, pop. And error message e02. Checked and changed ht lead to ignition bu
t still pops. With the casing on it seems to flex. Any idideas cheers also purged gas


Read more: http://www.ukplumbersforums.co.uk/central-heating-forum/44799-keston-c55-advice.html#ixzz2F3MYXruJ
 
What state is the burner seal in? Had similar fault when 1st serviced this model. And every year I have to replace the seal as its perished.
 