hi any chance could get a bit of advice please. changed two radiators today. and after filling up and bleeding all seemed fine. no leaks. then whent out for about an hour and half and came back to a cold house. stat in front room calls for heat but nothing happens at boiler end? but have dhw???? checked pump and seems fine. dont know what to do? cold house and poorley lad. any adfvice guys
thanx in advance
 
are the rest of the radiators fine ??? could be more air in the actull pipework leading to the radiators? did u open the TRVs fully and the lockshield valve???

close the TRV & lockshield, disconnect the nut between radiator and TRV get a pot under it and open TRV for about 10 seconds! do the same with the lockshield!
Make sure the pumps running while doing this?
 
sorry ive just re-read this, is the boiler not firing up for ch??
 
thank. forgot to mention its a heatline solarice 30 pc and think its something to do with wireless thermostat/clock
 
Last edited by a moderator:
is the new radiator installed close to this? if you think its this, remove the link in the boiler try it with just the boiler controls.
 
works with boiler timer clock. i had a similar problem with this last year but cant remember how i resolved it. think i called a guy in . changed batteries in room stat. . all rads are fully open with trv's.
 
works with boiler timer clock. i had a similar problem with this last year but cant remember how i resolved it. think i called a guy in . changed batteries in room stat. . all rads are fully open with trv's.

then the room stat is most likely your problem...
 
thanx for your help. much apreciated. i'm more anoyed with my self really for buying such a naff boiler. but suppose i can only go on peoples advice and maybe i listned to the wrong people.
thanx again
rich
 