J

johno_uk

Went to the above boiler last week, it kept blowing fuses. On looking at it, it was the div valve pin leaking onto the motor. I used the service kit and replaced the guts of the valve and the valve motor. Ran the boiler and tested hw and htg =happy days.

I got a recall today as the customer says the hw only gets Luke warm unless the heating is on??? I went round and the hw comes on when the tap opens as expected and the water heats to what I thought was not bad at all. But the customer was addement it was like "fire water" before it started tripping out last week. I tried to explain that the boiler can only heat upto a certain temp rise etc etc. then he put the heating on and To be fair when he ran the heating and then opened the hw tap, it was coming out hotter? When only the hw is on, the flow and return from the main hex into the plate you can hold without burning your hand. When heating is on it's too hot to touch. I would of expected it to be other way round with it firing on max rate on hw demand?

I didn't have long to look at it tonight but the hw thermistor was fine. I'll gas rate it and recheck pressures again tomorrow (we're fine after changing parts last week) failing that I'm putting it down to scaled up plate as its 6yrs old and there's no scale reducer filter fitted.

Been a long day, Any ideas or suggestions welcome. Luckily don't come across many aristons.

cheers
 
last time i changed those springs under the actuator it released loads of crap into the plate hex, did you change the bottom spring as well

sorry just re read your post, not sure if what i said is relevant

did you make sure everything was lined up, if you take the flow pipe off the manifold and shine a touch down you can double check its gone together as it should
 
Last edited:
Thanks for reply. I think it only goes in one way, it fit in securely and doesnt leak? Will check out the flow pipe on manifold to see if it looks ok. Cheers
 
Status
Not open for further replies.

Reply to Ariston ACO 32 MFFI Combi - hw only warm unless htg on in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
432
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason...
Replies
3
Views
328
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock