Discuss Not enough Heat in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
W

Wagger

We have recently had oil fired central heating installed.
All radiators have TRVs. We also have a system thermostat inthe hall, set at 25 degrees.
When the heating is first switched on all radiators becomehot or very hot but our rooms and the main thermostat reach only 19/21 degrees.After around 2 hours the radiators furthest from the boiler start to cool andwhile they warm up intermittently the rooms never get above 19/21. All TRVs areset at 5.
The system has been balanced and we are satisfied that thisis not a boiler problem. Our plumber is stumped. Any ideas?
 
i would disconect the room stat and see if the rooms get hot then if they do its a romstat positioning problem if they dont its either rads pipework or boiler to small
 
if boiler is still fired and furthest rad is cold not the room stat
 
Was the system designed (radiator sizes and boiler size) to work at 25 degrees?

Is 5 the maximum on the TRV?

Is the boiler cycling on and off when the temperature is 19 / 21 or is it running continuously?
 
Thanks. It looks wired in and I don't know how to disconnect it. However, the stat has been replaced and made no difference. We also tried increasing the temp with a hair drier and were able to do so. Of course, it could be a problem with the connection as the stat is wired into a complicated box and I don't know what is happening in there.
 
Thanks Snowhead. Answers : I don't know for certain but it should be OK . However, I suspect in some rooms the radiator may be too small although not in others where ther is the same problem.
Yes 5 is the max.
Boiler is cycling on and off when at 19/20
 
We have recently had oil fired central heating installed.
All radiators have TRVs. We also have a system thermostat inthe hall, set at 25 degrees.
When the heating is first switched on all radiators becomehot or very hot but our rooms and the main thermostat reach only 19/21 degrees.After around 2 hours the radiators furthest from the boiler start to cool andwhile they warm up intermittently the rooms never get above 19/21. All TRVs are set at 5.
The system has been balanced and we are satisfied that this is not a boiler problem. Our plumber is stumped. Any ideas?
What was the design temperature of the system? 21C is the norm. If you don't know, ask the system designer/installer.

What is the outside temperature? Most systems are designed assuming it is -1C or -3C.

Which boiler do you have - make and exact model?

How do you know the system has been correctly balanced?
 
Modulating. New super efficient boilers can recognise demand and adjust output accordingly. Previously humans brains did a similar but less complicated function by adjusting thermostatic control knob. As the brain of a boiler is zero the propensity to malfunction is now included by design.
 
Status