Prepare for a long story/process....
Open vented system no longer heats downstairs radiators.
No thermastatic valves just manual.
Boiler downstairs, BAXI, seems to work fine

I am a DIYer, Homeowner just over 1 year.
Moved in, heating was fine.
Then some blew up in the airing cupboard.
After 8 homeserver visits and a compensation cheque for their lack of skills..
The motor has been replaced twice
The diverter valve 3 times
HW tank stat twice
Room thermastat once
Whole system drained twice.
Eventually the electrical problem was fixed

Since then, we no longer get heating downstairs, their last visit "there must be a blockage caused by sludge". This is when i sacked them off and looked into this myself.

I've removed and flush out EVERY radiator in the house (Yes, they did have a fair amount of sludge in, now removed) I placed them back in and bled the air. Still no heat downstairs.

So i drained the system down as much as i could, every radiator open, doing this, i found that even though the water stopped coming out, if i went to another downstairs radiator, it was full of water?? This may be normal, or this might be part of the issue?

This is when i also added a Magiclean filter to the system, on the pipe between outlet of the pump and diverter valve. I bought 2m of pipe and ended up with 1.3m left, only used around 30cm but there was a lot of trial and error with fitting due to very tight space. This thing is working a treat, up to now it has cleaned a good amount (nothing compared to what i manually flushed out, it would have taken months of cleaning for the filter to do the same job if at all)

Once drained, i cleaned the header tank, added 2 liters of 800x cleaning solution (I have 9 radiators, most single but some double) so this should have been more than enough. Let everything fill up and bled the air, ran for 24 hours, mostly with heat, but at night i turned off the boiler and left pump running.
Next day i went around to each radiator at a time, attached hose to downstairs radiator, left the top tank filling ON, and left the pump on.
My idea was to keep adding fresh water to the system whilst draining each downstairs radiator, diluting the chemical in the system (Not letting the header tank get low) did this for around 2 hours.
Then drained the whole system. again, downstairs radiators still had water in them? so drained them manually as well.

Added neutralister to the header tank, let everything fill up, bled and ran for 1 week.

Still no heat downstairs!:(

So i learned about air locks.
Upstairs rads were fine and bled, so turned them all off at just 1 side as normal.

One at a time, isolated each radiator, bled out pressue, removed whole bleed nut(i think its called) attached a plastic nut to hose adapter.
Then i opened one side of the radiator fully for a few seconds, from what i can tell, a few bubles came out, turned that side off, did the other side.
Moved on to the next rad.

Every time i did this, hot water came through one side as expected, so the hot feed must be fine.
The cold side also generated high pressure as expected.

So this is where i am up to.
All upstairs radiators turned off, no heat downstairs.
Hot and cold feed seem to be fine to me.
pump seems to be working fine.

I have no idea what to do, the hot water is being pushed into the radiators, the cold water will flow backwards at force, so i assume the pipe isn't blocked.

Any ideas or questions extremely appriciated :)

Magiclean 1.jpeg


Magiclean 2.jpeg


Magiclean 3.jpeg


Magiclean 4.jpeg
 
ok Snc...can you put up a diagram of your system as you reckon it is...just biro one will do...include the boiler, the pump etc and any 3 way valves etc. crucially are the defuct rads
on the main system or is upstairs on a diff loop than that below or are the dstairs all dropped. centralheatking
 
So with all the rads upstairs turned off what happens

Rad trvs get warm anything ?
 
Do you have a separate thermostat for the heating downstairs, the system may be zoned with another 2 port valve somewhere. If so, you would have two room thermostats.

Or perhaps there's a gate valve on the return from the downstairs heating system somewhere. How old is the house? Could also be an old non return valve on some pipe work somewhere thats blocked or stuck shut.
 
This is the heating plan as far as i am aware.
All upstairs rads off - 2 rads downstairs kinda warm, 3 main ones stone cold.

I am sure the pump is working, as i've opened drain valves on lower rads with and without the pump on and i'm confident it is producing pressure when on.

@Steve weightman before all the cleaning, a magnet would stick to the water/air seperator in the aircupboard, i've just tested and it still does

@Jones82 It's only one zone for the whole house
House built in 1997 so not that old!

Like i said, i can isolate a rad downstairs, take out the nut from the top, put on a house and open each valve on the rad, one will give me flow hot water, other will give me flowing colder water, so the pipes going to them seem fine....

If there was for some reason a non return valve on the heating system, where would i look?

HEating.png
 
This is the heating plan as far as i am aware.
All upstairs rads off - 2 rads downstairs kinda warm, 3 main ones stone cold.

I am sure the pump is working, as i've opened drain valves on lower rads with and without the pump on and i'm confident it is producing pressure when on.

@Steve weightman before all the cleaning, a magnet would stick to the water/air seperator in the aircupboard, i've just tested and it still does

@Jones82 It's only one zone for the whole house
House built in 1997 so not that old!

Like i said, i can isolate a rad downstairs, take out the nut from the top, put on a house and open each valve on the rad, one will give me flow hot water, other will give me flowing colder water, so the pipes going to them seem fine..

If there was for some reason a non return valve on the heating system, where would i look?

View attachment 39018
The place I found a blockage was on the pump isolation valve and an amount of pipe just before it . I found all rads downstairs weren't working and also cleaned all the rads with system cleaner
 
Id still be looking at pump or a partial blockage, heat rises.

I think you would benefit from a visit from a recommended engineer.

Do you have any recourse with homeserve ie you’ve paid and they’ve not delivered.
 
Id still be looking at pump or a partial blockage, heat rises. You may get “pressure” as you put it but you’ll also be getting head of pressure from the tanks in the loft

I think you would benefit from a visit from a recommended engineer.

Do you have any recourse with homeserve ie you’ve paid and they’ve not delivered.
 
Id still be looking at pump or a partial blockage, heat rises.

I think you would benefit from a visit from a recommended engineer.

Do you have any recourse with homeserve ie you’ve paid and they’ve not delivered.

tbh that sounds about right, with the amount i've done and checked.
Luckily heating is covered through TSB home insurance, if the heating breaks, they come out for free. Unfortunatly, it is homeserver TSB use for these call outs. So i've lost 4 full days as holidays, could be worse, but it shouldn't have taken 7 visits to diagnose an electrical issue with the room thermistat.
 
Are you closing the bypass when you're turn the rads off upstairs also?

Otherwise it'll just sail round the bypass if downstairs are air locked.

Edit: Sorry from the diagram I assumed there was one, but there isn't from what I can see on pictures.
 
Prepare for a long story/process..
Open vented system no longer heats downstairs radiators.
No thermastatic valves just manual.
Boiler downstairs, BAXI, seems to work fine

I am a DIYer, Homeowner just over 1 year.
Moved in, heating was fine.
Then some blew up in the airing cupboard.
After 8 homeserver visits and a compensation cheque for their lack of skills..
The motor has been replaced twice
The diverter valve 3 times
HW tank stat twice
Room thermastat once
Whole system drained twice.
Eventually the electrical problem was fixed

Since then, we no longer get heating downstairs, their last visit "there must be a blockage caused by sludge". This is when i sacked them off and looked into this myself.

I've removed and flush out EVERY radiator in the house (Yes, they did have a fair amount of sludge in, now removed) I placed them back in and bled the air. Still no heat downstairs.

So i drained the system down as much as i could, every radiator open, doing this, i found that even though the water stopped coming out, if i went to another downstairs radiator, it was full of water?? This may be normal, or this might be part of the issue?

This is when i also added a Magiclean filter to the system, on the pipe between outlet of the pump and diverter valve. I bought 2m of pipe and ended up with 1.3m left, only used around 30cm but there was a lot of trial and error with fitting due to very tight space. This thing is working a treat, up to now it has cleaned a good amount (nothing compared to what i manually flushed out, it would have taken months of cleaning for the filter to do the same job if at all)

Once drained, i cleaned the header tank, added 2 liters of 800x cleaning solution (I have 9 radiators, most single but some double) so this should have been more than enough. Let everything fill up and bled the air, ran for 24 hours, mostly with heat, but at night i turned off the boiler and left pump running.
Next day i went around to each radiator at a time, attached hose to downstairs radiator, left the top tank filling ON, and left the pump on.
My idea was to keep adding fresh water to the system whilst draining each downstairs radiator, diluting the chemical in the system (Not letting the header tank get low) did this for around 2 hours.
Then drained the whole system. again, downstairs radiators still had water in them? so drained them manually as well.

Added neutralister to the header tank, let everything fill up, bled and ran for 1 week.

Still no heat downstairs!:(

So i learned about air locks.
Upstairs rads were fine and bled, so turned them all off at just 1 side as normal.

One at a time, isolated each radiator, bled out pressue, removed whole bleed nut(i think its called) attached a plastic nut to hose adapter.
Then i opened one side of the radiator fully for a few seconds, from what i can tell, a few bubles came out, turned that side off, did the other side.
Moved on to the next rad.

Every time i did this, hot water came through one side as expected, so the hot feed must be fine.
The cold side also generated high pressure as expected.

So this is where i am up to.
All upstairs radiators turned off, no heat downstairs.
Hot and cold feed seem to be fine to me.
pump seems to be working fine.

I have no idea what to do, the hot water is being pushed into the radiators, the cold water will flow backwards at force, so i assume the pipe isn't blocked.

Any ideas or questions extremely appriciated :)

View attachment 39012

View attachment 39013

View attachment 39014

View attachment 39015
I want to take you back to...
'something blew in the cupboard' then you called homeserve..up till then your ch was operating ok ? but they did not fix it...yes. The liability really lies with them who knows what their numpty has done...centralheatking
 
No i'm not, did know about this.
i'm not sure where this would be, i'll take a few pics as i've only got 3 gates to choose from

Sorry I edited my post after that. I thought from the technical diagram you had a bypass but from the images it doesn't seem you did.

When closing the upstairs rads, do you also close the gate valve on the return from the cylinder too? (I'm assuming you've also got just the heating on, not HW also). Also what speed is the pump set on.
 
Also the way it’s piped up, the cylinder coil can’t vent of air. I’d be inclined to remove that compression elbow with a tee and on a vertical piece of pipe, install a auto air vent
 
Also the way it’s piped up, the cylinder coil can’t vent of air. I’d be inclined to remove that compression elbow with a tee and on a vertical piece of pipe, install a auto air vent

Do you mean this gate valve on the straight pipe?
And then T off this bit and add an auto air vent at which point?

Gate valve.jpeg


Air vent.jpeg
 
Unfortunatly any further back or to the side and everything is covered by the pump and filter or cylinder.

No that's better. From your first image it only looked like there was two pipes coming from below, when there is 3. Cylinder return is correct, have you tried closing the gate valve on the cylinder, (The red one on the 15mm pipe) when turning off all the rads upstairs. There's a chance the MV isn't closing on HW or sneaking round the HW circuit when you're trying to force the heat downstairs.

Also bogrodders advice of installing an auto air vent would help vent any air from the coil.
 
Thanks for your help guys.
Like @bodrogger said, i will check that gate valve to see if it's cutting off flow and install auto vent whilst it's drained.

What is your advice for just draining the coil?
I can turn off the flow to the diverter valve, as well as the flow out of the coil. So does that mean i only have to deal with the amount of water in the coil in the tank? So i would just loosen it, let it drain a bit and be good to go.

Also any idea why there are two pipes here ? i would have thought just 1 goes back to the boiler

WhatsApp Image 2019-06-08 at 18.54.26.jpeg
 
So if you start from the front working to the back with the pipes along the wall you've got,

1) Return to boiler (The tee is the cylinder return)
2) Flow from boiler
3) Return from rads (22mm coming up from floor elbowing across)
4) Flow to rads (The one with the red arrow pointing down)
 
So if you start from the front working to the back with the pipes along the wall you've got,

1) Return to boiler (The tee is the cylinder return)
2) Flow from boiler
3) Return from rads (22mm coming up from floor elbowing across)
4) Flow to rads (The one with the red arrow pointing down)

Ahh makes perfect sense, i assumed the return from the rads would be under the floor somewhere, spot on thanks :)
 
This is the heating plan as far as i am aware.
All upstairs rads off - 2 rads downstairs kinda warm, 3 main ones stone cold.

I am sure the pump is working, as i've opened drain valves on lower rads with and without the pump on and i'm confident it is producing pressure when on.

@Steve weightman before all the cleaning, a magnet would stick to the water/air seperator in the aircupboard, i've just tested and it still does

@Jones82 It's only one zone for the whole house
House built in 1997 so not that old!

Like i said, i can isolate a rad downstairs, take out the nut from the top, put on a house and open each valve on the rad, one will give me flow hot water, other will give me flowing colder water, so the pipes going to them seem fine..

If there was for some reason a non return valve on the heating system, where would i look?

View attachment 39018

I’m assuming it’s just your diagram, but according to that, on the ground floor, you have a flow in one side with no return, and a return with no flow or the flow and return from one rad at the same end?
 
Personally I would say remove gate valve under the 3 way valve as there is no need to have that there.

I would doubt that the pump would be running slow as it looks like a ups pump so not very old but there is a possibility.

Those air seperators are shocking and do block up but from experience they limit the amount of cold coming in so they suck loads of air in. But I wouldnt say that is your problem.

You will have a blockage somewhere shut off all rad valves throughout the house drain 1 of the culprit rads open flow then return see if water stops if water flows but slows down you have a partial blockage somewhere give the system a good powerflush to try and remove the blockage.
 

Reply to No heat downstairs since Homeserve 'fixed' it in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
337
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock